Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Jul 1, 2024 at 12:33 PM,  <Steve Leyton 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> Living in the Pacific time zone means that I’m usually late to the party, but 
> Kyle just hit on what I was going to add to this conversation.             
> Per fire code, this building has a minimum fire flow requirement of 1,500 gpm 
> with reduction for sprinklers, and depending on gross area, it may be more.   
>  I don’t want to veer too far off topic here, but we have an INSIDIOUS 
> problem with water supply deterioration in San Diego and this may well be an 
> endemic issue on a broader scale.      When I started in the trade (an era 
> now known as the Before Times), much of SoCal’s water systems were brand new 
> and the expansion of our suburban built environment meant that infrastructure 
> had to be developed to facilitate growth, especially in LA, Orange and San 
> Diego Counties.      Many of the water systems were commissioned with well 
> over 100 psi static pressures and high-high residuals and 6,000 gpm flow 
> capabilities.    These have diminished due to increased demand as more and 
> more meters are connected to these zones, and also because some of the zones 
> with especially high pressures have actually been “turned down” by the 
> systems operators (both muni and private), because they found over time that 
> 120 psi residual pressure leads to all sorts of surge- and hammer-related 
> fatigue and maintenance issues.
>
>   
>
>   
>
>   
>
> The problem,    as you have here, is that if the owners of properties 
> affected by these changes aren’t informed by the water purveyors that they 
> now have 40-60 less psi of working pressure.    No much you can do about 
> organic pressure drops, but when the sysop intentionally reduces the pressure 
> and doesn’t advise its ratepayers…      like, wow.      And this is going on 
> right now in my home region.      Try to explain to a property owner that 
> they may have to put in a fire pump because the fire official that serves 
> them is holding them accountable for the operational strategies of the water 
> department that serves them, and they’re the SAME municipality.       Seems 
> to me that there’s a helluva    bruhaha a’ brewing.
>
>   
>
>   
>
>   
>
> Back to this one – if the FD can’t draw 1,000 gpm from the public water 
> supply, then THAT is what needs to be investigated.      I know that we’re 
> all in the business of selling work, but there’s more than a touch of 
> Stockholm Syndrome in the acceptance of this fate by both ownership and the 
> fire protection community.      I’m a consultant, so my first advice to this 
> owner would be get a stool and take it to city hall and go from department to 
> department – fire, water, economic development, city attorney – and get up on 
> that stool and start screaming as loudly as possible that this agency or that 
> agency has put them in a corner that will cost 6-figures that they’ve not 
> been reserving in the operation of this building.      Even if the owner has 
> religiously kept up an NFPA 25 ITM program, there would have been NOTHING 
> they could do to mitigate or pre-empt this deficiency and it’s most certainly 
> not the responsibility of private property owners to assure that the water 
> purveyor and serving fire department are on same page regarding the delivery 
> of adequate fire flow.
>
>   
>
>   
>
>   
>
> The code hasn’t changed, it’s the water supply that dropped.      Code says 
> the building owner must maintain fire/life safety systems in accordance with 
> codes and standards in effect when the building was certified for occupancy, 
> unless use and occupancy class change.      Has the occupancy class changed, 
> or is the building still being used for what it was originally certified for? 
>      If no change, then what I would do (advising the owner as a consultant, 
> or as the owner myself) is to respectfully send a letter to the city attorney 
> or city manager depending on type of government model, and respectfully 
> decline to conform to any notice of correction that I received.      If the 
> building was approved with a manual standpipe, and it’s still 4-stories high 
> and hasn’t changed use, then it’s still required to have a manual standpipe.  
>          The fire official is not empowered to make a code exception and 
> require them to have an automatic one and I’d call them on that.        If 
> you want to get involved that’s your choice, but if you start down this path 
> you are incurring potential liability that I personally would not touch.     
>
>   
>
>   
>
>   
>
> This sh*t is starting to make me mental…
>
>   
>
>   
>
>   
>
> Steve L.
>
>   
>
>   
>
>   
>   
>   
>
> From:   Kyle.Montgomery  <[email protected]>
>   Sent:  Monday, July 01, 2024 9:05 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: [External]Re: Water Tank for Standpipe
>
>   
>   
>   
>
>   
>
>   
>
> Agreed. Also, if they can’t support a manual standpipe calculation, how are 
> they able to support the site fire flow requirements? That’s usually at least 
> 1,000 GPM, and often much greater.
>
>   
>
>   
>
>   
>
>  Kyle Montgomery
>
>   
>
>     
>
>   
>
>  Aero Automatic Sprinkler Co.
>
>   
>
>  21605 N. Central Ave.
>
>   
>
>  Phoenix, AZ 85024
>
>   
>
>  Direct: 623.580.7820
>
>   
>
>  Cell: 602.763.4736
>
>   
>
>   [email protected] (mailto:[email protected])
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Ken Wagoner  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Monday, July 1, 2024 8:09 AM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  [External][Sprinklerforum] Re: Water Tank for Standpipe
>
>   
>   
>   
>
>   
>
>   
>
> What Cliff said.
>   
>  Among the issues I have to suggest you ask is "why" the city supply has 
> diminished.    And, as always, I agree with Cliff, it's likely not the 
> responsibility of the building owner (school district?) to sort out the "why" 
> issues.
>   
>  hope this helps,
>
>   
>   
>
> Ken Wagoner, SET
>   Parsley Consulting
>   500 West Mechanic Street
>   Harrisonville, Missouri 64701-2235
>   Phone: (760) 745-6181
>    Visit the website 
> (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1)
>
>   
>
>   
>
>   
>   
>   
>
> On 7/1/2024 10:03 AM,  [email protected] (mailto:[email protected])  
> wrote:
>
>   
>   
> >   
> >
> >  Hi Brian,
> >
> >   
> >
> >     
> >
> >   
> >
> >  I may be completely off base on this    but, if the city supply can’t 
> > supply 1000 gpm to the site and it could at some point in time, it sounds 
> > like they have an issue with their underground piping.    They need to 
> > start looking for a partially closed isolation valve in their system.    
> > It’s either that or an obstruction in their line.    Either way, I don’t 
> > think it’s the building owner’s responsibility to solve the City’s issue.
> >
> >   
> >
> >     
> >
> >   
> >   
> >
> >  Cliff Whitfield, SET
> >
> >   
> >
> >  President
> >
> >   
> >
> >     
> >
> >   
> >
> >  Fire Design, Inc.
> >
> >   
> >
> >  940 Summerbrooke Dr
> >
> >   
> >
> >  Tallahassee, FL 32312
> >
> >   
> >
> >  Ph: 828-284-4772
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> >     
> >
> >   
> >   
> >   
> >
> > From:   Brian Harris  <[email protected]> 
> > (mailto:[email protected])
> >   Sent:  Monday, July 1, 2024 10:57 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected]> 
> > (mailto:[email protected])
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >
> > Mostly volume, slight pressure.
> >
> >   
> >
> >   
> >
> >   
> >   
> >
> >  Thank you,
> >
> >   
> >
> >     
> >
> >   
> >
> >  Brian Harris, CET
> >
> >   
> >
> >  BVS Systems Inc.
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> > From:   Fpdcdesign  <[email protected] (mailto:[email protected])>
> >   Sent:  Monday, July 1, 2024 9:55 AM
> >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > <[email protected] 
> > (mailto:[email protected])>
> >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> >
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >
> > Volume or pressure?
> >
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >
> > Todd Williams   
> >
> >   
> >   
> >
> > Fire Protection Design/Consulting
> >
> >   
> >   
> >   
> >
> > Stonington, CT
> >
> >   
> >   
> >   
> >
> > 860-608-4559
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >
> >   
> >
> >
> >   
> > >   
> > >   
> > >
> > > On Jul 1, 2024 at 9:25 AM,  <Brian Harris 
> > > (mailto:[email protected])>  wrote:
> > >
> > >   
> > >   
> > >   
> > >
> > > Todd-
> > >
> > >   
> > >
> > > Yes, it’s a manual wet standpipe. Problem is the city supply has dropped 
> > > a fair amount and now the standpipe test won’t pass.
> > >
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >
> > >  Thank you,
> > >
> > >   
> > >
> > >     
> > >
> > >   
> > >
> > >  Brian Harris, CET
> > >
> > >   
> > >
> > >  BVS Systems Inc.
> > >
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >
> > > From:   Fpdcdesign  <[email protected] (mailto:[email protected])>
> > >   Sent:  Monday, July 1, 2024 9:21 AM
> > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > <[email protected] 
> > > (mailto:[email protected])>
> > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > >
> > >   
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >
> > > Isn’t this a 4 story building? Below the high rise threshold, I assume. 
> > > Can it be a manual wet standpipe?   
> > >
> > >   
> > >   
> > >
> > >   
> > >
> > >   
> > >   
> > >   
> > >   
> > >
> > > Todd Williams   
> > >
> > >   
> > >   
> > >
> > > Fire Protection Design/Consulting
> > >
> > >   
> > >   
> > >   
> > >
> > > Stonington, CT
> > >
> > >   
> > >   
> > >   
> > >
> > > 860-608-4559
> > >
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >   
> > >
> > >
> > >   
> > >   
> > >
> > >
> > >   
> > > >   
> > > >   
> > > >
> > > > On Jul 1, 2024 at 9:09 AM,  <Paul Kimble (mailto:[email protected])> 
> > > >  wrote:
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > Has anyone done a valued engineering survey of the city water supply 
> > > > and compared the original water test provided to the current. Is the 
> > > > city supply a gravity fed system or a system utilizing pumps? There may 
> > > > have been a pump down when you performed your last test or there maybe 
> > > > valves within the city supply that are partially open causing your 
> > > > loss.    
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >
> > > > Paul D. Kimble
> > > >
> > > >   
> > > >
> > > > VP Operations
> > > >
> > > >   
> > > >
> > > > A.S. Barlin Associates, Inc.
> > > >
> > > >   
> > > >
> > > >  [email protected] (mailto:[email protected])
> > > >
> > > >   
> > > >
> > > > (973) 696-6601 Office
> > > >
> > > >   
> > > >
> > > > (973) 632-8341 Cell
> > > >
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > From:   Eric Rieve  <[email protected] (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 8:27 AM
> > > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Brian,
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > I have the feeling that messing around with something complicated like 
> > > > a break-tank and having to rearrange your fire pump wouldn’t be worth 
> > > > it compared to simply installing a 30-minute duration dry hydrant on 
> > > > the property. It would be a lot larger tank but would guarantee you 
> > > > have a dedicated water supply volume just for standpipes.
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > If your city water supply has already lost 25% of it’s capacity, trying 
> > > > to design a work-around based on the new number is just setting the 
> > > > property up for having to go through the entire exercise again when the 
> > > > supply gets even worse. Taking the standpipe demand out altogether also 
> > > > benefits the sprinkler system’s design longevity since you’ll have 
> > > > significantly reduced the demand going forward.
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Just my two cents.
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Hope this helps,
> > > >
> > > >   
> > > >
> > > > Eric Rieve, SET
> > > >  Rieve Fire Protection
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > From:   Brian Harris  <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 7:53 AM
> > > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Travis-
> > > >
> > > >   
> > > >
> > > > Yes,  &  yes. My question was since the system was designed and 
> > > > installed the water supply now is about 3/4 of what it was. We are 
> > > > looking to supplement the city supply with a water tank since the fire 
> > > > truck shuts down before we can get the 1000gpm. The city supply is 
> > > > running out of water. I was curious as to the sizing of a supplemental 
> > > > tank. I see if it’s only supplied by a tank, it needs a 30-minute 
> > > > duration. Since the city is capable of supplying “most” of the demand I 
> > > > looking for the best way would be to properly size a tank.
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >
> > > >  Thank you,
> > > >
> > > >   
> > > >
> > > >     
> > > >
> > > >   
> > > >
> > > >  Brian Harris, CET
> > > >
> > > >   
> > > >
> > > >  BVS Systems Inc.
> > > >
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > From:   Travis Mack  <[email protected] (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 7:45 AM
> > > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > I doubt that school is tall enough to    be a high rise. Manual is 
> > > > allowed per NFPA 14. Do you know what a manual standpipe is? If so, 
> > > > contact the AHJ to find out what they require you use as a supply 
> > > > value.    A manual standpipe has its supply as the FDC. So calculate as 
> > > > the FDC as your supply with the values the ahj provides. It’s likely 
> > > > going to be something like 150 psi at 1000 gpm.   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > Travis Mack, SET
> > > >
> > > >   
> > > >
> > > > M.E.P.CAD   |   
> > > >
> > > >   
> > > >
> > > > 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> > > >
> > > >   
> > > >
> > > > www.mepcad.com (http://www.mepcad.com/)   |   m:   480.547.9348
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > AutoSPRINK    |    AutoSPRINK FAB    |    AutoSPRINK RVT    |    
> > > > AlarmCAD
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Book appointment time in my calendar
> > > >
> > > >   
> > > >
> > > > https://calendly.com/t_mack_mepcad
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > >  From:    Brian Harris  <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 4:38:05 AM
> > > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > >  Yasser
> > > >
> > > >   
> > > >
> > > >     
> > > >
> > > >   
> > > >
> > > >  Thank you,
> > > >
> > > >   
> > > >
> > > >     
> > > >
> > > >   
> > > >
> > > >  Brian Harris, CET
> > > >
> > > >   
> > > >
> > > >  BVS Systems Inc.
> > > >
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > From:   Yasser Amer Ahmed  <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 6:44 AM
> > > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Hi Brian,
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > As per NFPA-14, 5.2 (2024 Ed.) 5.2 Minimum Supply for Class I, Class D, 
> > > > and Class III Systems. The minimum water supply shall be capable of 
> > > > providing the system de1nand established by Chapter 10 for at least 30 
> > > > minutes.
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > All Gratitude,
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Yasser Amer Ahmed
> > > >
> > > >   
> > > >
> > > > Fire Protection  &  Plumbing Specialist
> > > >
> > > >   
> > > >
> > > > Registered Fire Protection Consultant
> > > >
> > > >   
> > > >
> > > > MBA,  LEED AP BD+C™, CPD, CFPS, MIFireE, PMSFPE
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Smart Village, Cairo-Alexandria Desert Road
> > > >
> > > >   
> > > >
> > > > Street 26, Building 10
> > > >
> > > >   
> > > >
> > > > P.O. Box: 129, Giza 12577, Egypt
> > > >
> > > >   
> > > >
> > > > Tel: +202 3531 8000
> > > >
> > > >   
> > > >
> > > > Fax: +202 3537 1223
> > > >
> > > >   
> > > >
> > > >   dar.com 
> > > > (https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=)
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > > (https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=)
> > > >
> > > >   
> > > >
> > > > Please consider the environment before printing this document
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > From:   Travis Mack  <[email protected] (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 1:34 PM
> > > >   To:  Discussion list on issues relating to automatic fire sprinklers  
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Re: Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >  ! External Email, Use Caution !
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > > Is it a high rise or mid rise? If mid rise, calc it to the FDC and be 
> > > > done. If a high rise and automatic standpipe, check NFPA 14. The 
> > > > duration is 30 minutes.    So that is how you would size a tank.   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > > Travis Mack, SET
> > > >
> > > >   
> > > >
> > > > M.E.P.CAD   |   
> > > >
> > > >   
> > > >
> > > > 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> > > >
> > > >   
> > > >
> > > >  www.mepcad.com 
> > > > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mepcad.com%2f&c=E,1,-4N2RZKUba_tdy65g6bmxh0QKzZyB4IFxh7FewvPS08dfMil9SJ7e-nULD3iv8Tco6tXDK1EfeIYVTl6v8gt_jeh3nwQJShLejhSBFPVdWqVOxQnapv-TMIHA6g,&typo=1)
> > > >    |   m:   480.547.9348
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > AutoSPRINK    |    AutoSPRINK FAB    |    AutoSPRINK RVT    |    
> > > > AlarmCAD
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Book appointment time in my calendar
> > > >
> > > >   
> > > >
> > > > https://calendly.com/t_mack_mepcad
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > >  From:    Brian Harris  <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Sent:  Monday, July 1, 2024 3:31:59 AM
> > > >   To:   [email protected] 
> > > > (mailto:[email protected])     
> > > > <[email protected] 
> > > > (mailto:[email protected])>
> > > >   Subject:  [Sprinklerforum] Water Tank for Standpipe
> > > >
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > > We have a project where the water supply has degraded a good bit since 
> > > > installation was completed. Sprinkler system and pump test all pass but 
> > > > the standpipe test runs out of water. Only thing I can think of to help 
> > > > would be a water tank but how would you even size one since the 
> > > > “duration” of a standpipe test is open ended? Any other thoughts?
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Thank you,
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > > Brian Harris, CET
> > > >
> > > >   
> > > >
> > > > BVS Systems Inc.
> > > >
> > > >   
> > > >
> > > >   bvssystemsinc.com 
> > > > (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,DxViP7dSzV-R2rx5fGIyoL1vsDK_tTbfrJamJJsCEkhMVaCVUXX3uMknt5ksggBpEfXELKFUusTuDEcjOcvs4e1Xf-ZA6si2AAvUiof7pgyIcg,,&typo=1)
> > > >
> > > >   
> > > >
> > > > Phone: 704.896.9989
> > > >
> > > >   
> > > >
> > > > Fax: 704.896.1935
> > > >
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >   
> > > >   
> > > >   
> > > >  Confidentiality  &  Disclaimer Note: This e-mail (including any 
> > > > attachments) contain protected and confidential information intended 
> > > > for the sole use of the individual or organization addressee. If you 
> > > > are not the addressee or an authorized agent acting on their behalf, or 
> > > > if you have received this message by error, please notify the sender 
> > > > immediately be returning the message. It must not be copied, 
> > > > distributed or used in any other way but should be immediately deleted 
> > > > from your system.
> > > >   
> > > >  While Dar and the Dar Group strive to maintain high standards of 
> > > > communication, reliability, authenticity and integrity, neither shall 
> > > > be liable for the improper or incomplete transmission of the 
> > > > information contained in this communication nor for any delay in its 
> > > > receipt or damage to your system. Neither Dar nor the Dar Group 
> > > > guarantees that the integrity of this communication has been maintained 
> > > > or that this communication is free of viruses, interceptions or 
> > > > interference.
> > > >   
> > > > Confidentiality  &  Disclaimer Note: This e-mail (including any 
> > > > attachments) contain protected and confidential information intended 
> > > > for the sole use of the individual or organization addressee. If you 
> > > > are not the addressee or an authorized agent acting on their behalf, or 
> > > > if you have received this message by error, please notify the sender 
> > > > immediately be returning the message. It must not be copied, 
> > > > distributed or used in any other way but should be immediately deleted 
> > > > from your system. While Dar and the Dar Group strive to maintain high 
> > > > standards of communication, reliability, authenticity and integrity, 
> > > > neither shall be liable for the improper or incomplete transmission of 
> > > > the information contained in this communication nor for any delay in 
> > > > its receipt or damage to your system. Neither Dar nor the Dar Group 
> > > > guarantees that the integrity of this communication has been maintained 
> > > > or that this communication is free of viruses, interceptions or 
> > > > interference.
> > > >
> > > >   
> > > >   
> > > >   
> > > >
> > > >  _________________________________________________________ 
> > > > SprinklerForum mailing list:   
> > > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > > >   To unsubscribe send an email to  
> > > > [email protected] 
> > > > (mailto:[email protected])
> > > >
> > > >   
> > > >   
> > >   
> > >   
> > >   
> > >
> > >  _________________________________________________________ SprinklerForum 
> > > mailing list:   
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >   To unsubscribe send an email to  
> > > [email protected] 
> > > (mailto:[email protected])
> > >
> > >   
> > >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >   
> >   
> >
> >   
> > (https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient)
> >
> >   
> >   
> >   
> >
> >  Virus-free.www.avast.com 
> > (https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient)
> >
> >   
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >
> >   
> >   
> >   
> >  _________________________________________________________  
> >   
> >  SprinklerForum mailing list:  
> >   
> >   
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >   
> >   
> >  To unsubscribe send an email to  
> > [email protected] 
> > (mailto:[email protected])   
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     