The limit for 0.2 is in the storage section. If you are not in storage, calc it and you are good.
Travis Mack, SET M.E.P.CAD | 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348 AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT | AlarmCAD Book appointment time in my calendar https://calendly.com/t_mack_mepcad ________________________________ From: Bobby Welch <[email protected]> Sent: Wednesday, July 31, 2024 4:11:17 PM To: [email protected] <[email protected]> Subject: [Sprinklerforum] Old pipe Schedule system I am working on a project that looks to be an old pipe scheduled system. the branch line schedule is 1”, 1”, 1.25”, 1.5”, 1.5”, 2” and the heads appear to be ½” 5.6K sprinklers. The spacing is 10’ x 10’ on the heads. There is a placard on the riser that states the area was calculated at a 0.60 over 2000 sq. ft., but it is newer I am assuming that this was put on the riser by mistake. From the type of heads and the spacing I would assume ordinary hazard is what this system was designed for. My question is there a limit to the design density for 5.6K sprinklers? It is my understanding that 5.6K sprinklers cannot be used for anything greater then a 0.20 density. Bobby Welch | Sprinkler Systems Designer KOORSEN FIRE & SECURITY 8090 N Dixie Dr, Dayton, OH 45414 P 937.641.8403 | Ext. 0318 | M 937.594.8457 [email protected]<mailto:[email protected]> | www.koorsen.com<http://www.koorsen.com> 24x7x365 Service: 937.660.7050 | [email protected]