NFPA 13, 2016

12.6.1 For storage applications with densities of 0.2 gpm/ft2 (8.1 mm/min)
or less, standard response
sprinklers with a K-factor of K-5.6 (80) or larger shall be permitted.

12.6.2 For general storage applications, rack storage, rubber tire storage,
roll paper storage,
and baled cotton storage being protected with upright and pendent spray
sprinklers with
required densities of greater than 0.2 gpm/ft2 to 0.34 gpm/ft2 (8.1 mm/min
to 13.9 mm/min),
standard-response sprinklers with a nominal K-factor of K-8.0 (115) or
larger shall be used.

12.6.3 For general storage applications, rack storage, rubber tire storage,
roll paper storage,
and baled cotton storage being protected with upright and pendent spray
sprinklers with
required densities greater than 0.34 gpm/ft2 (13.9 mm/min),
standard-response spray sprinklers
with a K-factor of K-11.2 (161) or larger that are listed for storage
applications shall be used.

12.6.4* Unless the requirements of 12.6.5 are met, the requirements of
12.6.2 and 12.6.3
shall not apply to modifications to existing storage application systems,
using sprinklers with
K-factors of K-8.0 (115) or less.

Thanks

I will be away from the office July 15, 16, 18, & 19, I will be available
only on Wednesday the 17th


Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca

Proudline now offers ULc listed monitoring services, please contact
[email protected] for more information






On Wed, Jul 31, 2024 at 3:12 PM Bobby Welch <[email protected]> wrote:

> I am working on a project that looks to be an old pipe scheduled system.
> the branch line schedule is 1”, 1”, 1.25”, 1.5”, 1.5”, 2” and the heads
> appear to be ½” 5.6K sprinklers. The spacing is 10’ x 10’ on the heads.
> There is a placard on the riser that states the area was calculated at a
> 0.60 over 2000 sq. ft., but it is newer I am assuming that this was put on
> the riser by mistake. From the type of heads and the spacing I would assume
> ordinary hazard is what this system was designed for. My question is there
> a limit to the design density for 5.6K sprinklers? It is my understanding
> that 5.6K sprinklers cannot be used for anything greater then a 0.20
> density.
>
> Bobby Welch | Sprinkler Systems Designer
>
> *KOORSEN FIRE & SECURITY*8090 N Dixie Dr, Dayton, OH 45414
> P 937.641.8403 | Ext. 0318 | M 937.594.8457
> [email protected] | www.koorsen.com
>
> *24x7x365 Service: 937.660.7050* | [email protected]
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to