Doesn’t NFPA 20 list a 400 gpm fire pump in the summary of centrifugal fire 
pumps? AC fire pump and many others sell a 400 gpm fire pump.


Travis Mack, SET

MEPCAD | Instructor / Training Specialist

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad


Academy of Fire Sprinkler Technology | Executive Director

101 S Main Street, Suite 001, Decatur, IL 62523


________________________________
From: Bob Caputo <[email protected]>
Sent: Monday, October 6, 2025 2:31:54 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [External]Multiple undersized pumps.

Are you sure you have a fire pump rated at 400 gpm?  Listed fire pumps come in 
250, 500, 750 etc gpm.  Not 400 gpm.  That aside, perhaps adding a water 
storage tank will solve the problem?

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p:      214-349-5965 ext124
w:      firesprinkler.org<http://firesprinkler.org/>
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org/>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://twitter.com/afsa/status/1039528345367732224>   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>  
 
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 <https://www.instagram.com/firesprinklerorg/>


Train a safer, more efficient workforce.

By enrolling your employees in the AFSA Apprenticeship Training Series for 
Sprinkler 
Fitters<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
 you will reap the benefits of a qualified, professional installation crew. 
Well-trained employees will work smarter, increasing your company's 
productivity and, in turn, its profits. Learn 
more<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>.


On Mon, Oct 6, 2025 at 11:23 AM Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:
Kyle, As I mentioned, there are several issues with this site I didn’t mention. 
One is approximately 1000 ft of 80 year old, severely tuberculated 8” main 
(estimate C=30) that feeds the site. The first thing is that this needs to be 
replaced. Once that is done, the 825 is very possible.

CW, I have all of that info. I have been working on this since 2021 and it just 
came back to life after a year away. 825 gpm is the sprinkler demand only. 
There is a raw water supply that would be used for hose streams.

I hesitate to post many specifics of the project here as what is going on could 
result in litigation.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)


On Oct 6, 2025 at 11:26 AM, <Kyle.Montgomery<mailto:[email protected]>> 
wrote:


“Neither pump has ever passed its initial test due to the water supply”. So, 
the water supply can’t even provide 600 GPM to the little pump? If that’s the 
case, there is no workaround other than adding a water tank. You can commission 
the pump without reaching 150% of the rated capacity, but you have to at least 
meet the demand flow and pressure. If you can’t get to 600 GPM, you certainly 
aren’t getting to 825 GPM.



-Kyle M at Aero



From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, October 6, 2025 7:24 AM
To: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Subject: [External][Sprinklerforum] Multiple undersized pumps.



I am working on a project for a facility with several small and medium sized 
buildings. Only some of the buildings are sprinklered. This location has a 
plethora of problems but I only have one that i will bring here.



The facility has a very bad water supply and a new building was constructed, 
complete with fire pump, to meet a demand of 825 gpm. Also on this site is a 
fire pump house with a 400 gpm at 75 psi pump that takes suction from the main. 
I was told this pump only feeds a dedicated main to 3 buildings. However, I 
subsequently found that the pump actually ties into the underground feeding the 
entire site, including the new building. Now I have a main fed by a pump with a 
maximum flow of 600 gpm feeding a 750 gpm pump. Is there any way to get this to 
work? There is no by-pass around the 400 gpm pump. Not sure if that would make 
a difference. I would appreciate input from those mightier than I.



Neither pump has ever passed its initial test due to the water supply.



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080<tel:860-535-2080> (ofc)

860-554-7054<tel:860-554-7054>  (fax)

860-608-4559<tel:860-608-4559> (cell)

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to