I am sitting g in an airport with a beer awaiting my flight back to Dallas
- not looking at a book so maybe I am wrong.

Bob Caputo, CFPS
*President*

*American Fire Sprinkler Association*
p: 214-349-5965 ext124
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Train a safer, more efficient workforce.*

By enrolling your employees in the AFSA Apprenticeship Training Series for
Sprinkler Fitters
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
you will reap the benefits of a qualified, professional installation crew.
Well-trained employees will work smarter, increasing your company's
productivity and, in turn, its profits. Learn more
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
.


On Mon, Oct 6, 2025 at 2:41 PM Bob Caputo <[email protected]> wrote:

> I’ve been wrong before….  I didn’t thing NFPA 20 listed other flows than
> the table in chapter 4
>
>
> Bob Caputo, CFPS
> *President*
>
> *American Fire Sprinkler Association*
> p: 214-349-5965 ext124
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Train a safer, more efficient workforce.*
>
> By enrolling your employees in the AFSA Apprenticeship Training Series
> for Sprinkler Fitters
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
> you will reap the benefits of a qualified, professional installation crew.
> Well-trained employees will work smarter, increasing your company's
> productivity and, in turn, its profits. Learn more
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
> .
>
>
> On Mon, Oct 6, 2025 at 2:35 PM Travis Mack <[email protected]> wrote:
>
>> Doesn’t NFPA 20 list a 400 gpm fire pump in the summary of centrifugal
>> fire pumps? AC fire pump and many others sell a 400 gpm fire pump.
>>
>> Travis Mack, SET
>>
>> *MEPCAD* | Instructor / Training Specialist
>>
>> 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
>> <https://www.google.com/maps/search/181+N.+Arroyo+Grande+Blvd.+%23105+I+Henderson,+NV+89074?entry=gmail&source=g>
>>
>> www.mepcad.com | *m: **480.547.9348*
>>
>>
>>
>> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>>
>>
>>
>> Book appointment time in my calendar
>>
>> https://calendly.com/t_mack_mepcad
>>
>>
>> *Academy of Fire Sprinkler Technology *| Executive Director
>>
>> 101 S Main Street, Suite 001, Decatur, IL 62523
>> <https://www.google.com/maps/search/101+S+Main+Street,+Suite+001,+Decatur,+IL+62523?entry=gmail&source=g>
>>
>>
>> ------------------------------
>> *From:* Bob Caputo <[email protected]>
>> *Sent:* Monday, October 6, 2025 2:31:54 PM
>> *To:* Discussion list on issues relating to automatic fire sprinklers <
>> [email protected]>
>> *Subject:* [Sprinklerforum] Re: [External]Multiple undersized pumps.
>>
>> Are you sure you have a fire pump rated at 400 gpm?  Listed fire pumps
>> come in 250, 500, 750 etc gpm.  Not 400 gpm.  That aside, perhaps adding a
>> water storage tank will solve the problem?
>>
>> Bob Caputo, CFPS
>> *President*
>>
>> *American Fire Sprinkler Association*
>> p: 214-349-5965 ext124
>> w: firesprinkler.org
>> <https://www.facebook.com/firesprinkler.org/>
>> <https://twitter.com/afsa/status/1039528345367732224>
>> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>>    <https://www.instagram.com/firesprinklerorg/>
>>
>> *Train a safer, more efficient workforce.*
>>
>> By enrolling your employees in the AFSA Apprenticeship Training Series
>> for Sprinkler Fitters
>> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
>> you will reap the benefits of a qualified, professional installation crew.
>> Well-trained employees will work smarter, increasing your company's
>> productivity and, in turn, its profits. Learn more
>> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
>> .
>>
>>
>> On Mon, Oct 6, 2025 at 11:23 AM Fpdcdesign <[email protected]> wrote:
>>
>> Kyle, As I mentioned, there are several issues with this site I didn’t
>> mention. One is approximately 1000 ft of 80 year old, severely tuberculated
>> 8” main (estimate C=30) that feeds the site. The first thing is that this
>> needs to be replaced. Once that is done, the 825 is very possible.
>>
>> CW, I have all of that info. I have been working on this since 2021 and
>> it just came back to life after a year away. 825 gpm is the sprinkler
>> demand only. There is a raw water supply that would be used for hose
>> streams.
>>
>> I hesitate to post many specifics of the project here as what is going on
>> could result in litigation.
>>
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860-535-2080 (ofc)
>> 860-554-7054  (fax)
>> 860-608-4559 (cell)
>>
>>
>> On Oct 6, 2025 at 11:26 AM, <Kyle.Montgomery <[email protected]>>
>> wrote:
>>
>> “Neither pump has ever passed its initial test due to the water supply”.
>> So, the water supply can’t even provide 600 GPM to the little pump? If
>> that’s the case, there is no workaround other than adding a water tank. You
>> can commission the pump without reaching 150% of the rated capacity, but
>> you have to at least meet the demand flow and pressure. If you can’t get to
>> 600 GPM, you certainly aren’t getting to 825 GPM.
>>
>>
>>
>> -Kyle M at Aero
>>
>>
>>
>> *From:* Fpdcdesign <[email protected]>
>> *Sent:* Monday, October 6, 2025 7:24 AM
>> *To:* Sprinklerforum <[email protected]>
>> *Subject:* [External][Sprinklerforum] Multiple undersized pumps.
>>
>>
>>
>> I am working on a project for a facility with several small and medium
>> sized buildings. Only some of the buildings are sprinklered. This location
>> has a plethora of problems but I only have one that i will bring here.
>>
>>
>>
>> The facility has a very bad water supply and a new building was
>> constructed, complete with fire pump, to meet a demand of 825 gpm. Also on
>> this site is a fire pump house with a 400 gpm at 75 psi pump that takes
>> suction from the main. I was told this pump only feeds a dedicated main to
>> 3 buildings. However, I subsequently found that the pump actually ties into
>> the underground feeding the entire site, including the new building. Now I
>> have a main fed by a pump with a maximum flow of 600 gpm feeding a 750 gpm
>> pump. Is there any way to get this to work? There is no by-pass around the
>> 400 gpm pump. Not sure if that would make a difference. I would appreciate
>> input from those mightier than I.
>>
>>
>>
>> Neither pump has ever passed its initial test due to the water supply.
>>
>>
>>
>> Todd G Williams, PE
>>
>> Fire Protection Design/Consulting
>>
>> Stonington, CT
>>
>> 860-535-2080 (ofc)
>>
>> 860-554-7054  (fax)
>>
>> 860-608-4559 (cell)
>> _________________________________________________________ SprinklerForum
>> mailing list:
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to