You’re correct.  Someone must have snuck those 300 and 400 gpm pumps into
the table while I was napping 🤣

Bob Caputo, CFPS
*President*

*American Fire Sprinkler Association*
p: 214-349-5965 ext124
w: firesprinkler.org
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
   <https://www.instagram.com/firesprinklerorg/>

*Train a safer, more efficient workforce.*

By enrolling your employees in the AFSA Apprenticeship Training Series for
Sprinkler Fitters
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
you will reap the benefits of a qualified, professional installation crew.
Well-trained employees will work smarter, increasing your company's
productivity and, in turn, its profits. Learn more
<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
.


On Mon, Oct 6, 2025 at 2:54 PM Travis Mack <[email protected]> wrote:

> Highly trust and value your opinion. Had to check to make sure I hadn’t
> been doing things wrong.
>
> Worse thing in this industry is “but that’s how we’ve always done it. “.
>
> Have a safe trip.
>
> Travis Mack, SET
>
> *MEPCAD* | Instructor / Training Specialist
>
> 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
> <https://www.google.com/maps/search/181+N.+Arroyo+Grande+Blvd.+%23105+I+Henderson,+NV+89074?entry=gmail&source=g>
>
> www.mepcad.com | *m: **480.547.9348*
>
>
>
> *AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD*
>
>
>
> Book appointment time in my calendar
>
> https://calendly.com/t_mack_mepcad
>
>
> *Academy of Fire Sprinkler Technology *| Executive Director
>
> 101 S Main Street, Suite 001, Decatur, IL 62523
> <https://www.google.com/maps/search/101+S+Main+Street,+Suite+001,+Decatur,+IL+62523?entry=gmail&source=g>
>
>
> ------------------------------
> *From:* Bob Caputo <[email protected]>
> *Sent:* Monday, October 6, 2025 2:50:29 PM
>
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Multiple undersized pumps.
>
> Like I said, I’ve been wrong before
>
> Bob Caputo, CFPS
> *President*
>
> *American Fire Sprinkler Association*
> p: 214-349-5965 ext124
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Train a safer, more efficient workforce.*
>
> By enrolling your employees in the AFSA Apprenticeship Training Series
> for Sprinkler Fitters
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
> you will reap the benefits of a qualified, professional installation crew.
> Well-trained employees will work smarter, increasing your company's
> productivity and, in turn, its profits. Learn more
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
> .
>
>
> On Mon, Oct 6, 2025 at 2:41 PM James Yost <[email protected]> wrote:
>
> Hello Bob-
>
>
>
> 300 and 400 GPM pumps are quite popular, listed and readily available!
>
>
>
>
>
> *From:* Bob Caputo <[email protected]>
> *Sent:* Monday, October 6, 2025 2:32 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Multiple undersized pumps.
>
>
>
> Are you sure you have a fire pump rated at 400 gpm?  Listed fire pumps
> come in 250, 500, 750 etc gpm.  Not 400 gpm.  That aside, perhaps adding a
> water storage tank will solve the problem?
>
> Bob Caputo, CFPS
>
> *President*
>
> *American Fire Sprinkler Association*
>
> p:
>
> 214-349-5965 ext124
>
> w:
>
> firesprinkler.org
>
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Train a safer, more efficient workforce.*
>
> By enrolling your employees in the AFSA Apprenticeship Training Series
> for Sprinkler Fitters
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
> you will reap the benefits of a qualified, professional installation crew.
> Well-trained employees will work smarter, increasing your company's
> productivity and, in turn, its profits. Learn more
> <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>
> .
>
>
>
>
>
> On Mon, Oct 6, 2025 at 11:23 AM Fpdcdesign <[email protected]> wrote:
>
> Kyle, As I mentioned, there are several issues with this site I didn’t
> mention. One is approximately 1000 ft of 80 year old, severely tuberculated
> 8” main (estimate C=30) that feeds the site. The first thing is that this
> needs to be replaced. Once that is done, the 825 is very possible.
>
>
>
> CW, I have all of that info. I have been working on this since 2021 and it
> just came back to life after a year away. 825 gpm is the sprinkler demand
> only. There is a raw water supply that would be used for hose streams.
>
>
>
> I hesitate to post many specifics of the project here as what is going on
> could result in litigation.
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
>
>
>
>
> On Oct 6, 2025 at 11:26 AM, <Kyle.Montgomery <[email protected]>>
> wrote:
>
> “Neither pump has ever passed its initial test due to the water supply”.
> So, the water supply can’t even provide 600 GPM to the little pump? If
> that’s the case, there is no workaround other than adding a water tank. You
> can commission the pump without reaching 150% of the rated capacity, but
> you have to at least meet the demand flow and pressure. If you can’t get to
> 600 GPM, you certainly aren’t getting to 825 GPM.
>
>
>
> -Kyle M at Aero
>
>
>
> *From:* Fpdcdesign <[email protected]>
> *Sent:* Monday, October 6, 2025 7:24 AM
> *To:* Sprinklerforum <[email protected]>
> *Subject:* [External][Sprinklerforum] Multiple undersized pumps.
>
>
>
> I am working on a project for a facility with several small and medium
> sized buildings. Only some of the buildings are sprinklered. This location
> has a plethora of problems but I only have one that i will bring here.
>
>
>
> The facility has a very bad water supply and a new building was
> constructed, complete with fire pump, to meet a demand of 825 gpm. Also on
> this site is a fire pump house with a 400 gpm at 75 psi pump that takes
> suction from the main. I was told this pump only feeds a dedicated main to
> 3 buildings. However, I subsequently found that the pump actually ties into
> the underground feeding the entire site, including the new building. Now I
> have a main fed by a pump with a maximum flow of 600 gpm feeding a 750 gpm
> pump. Is there any way to get this to work? There is no by-pass around the
> 400 gpm pump. Not sure if that would make a difference. I would appreciate
> input from those mightier than I.
>
>
>
> Neither pump has ever passed its initial test due to the water supply.
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to