I'm a bit confused on whether sprinklers are required or not in an attic with fuel fired equipment.

Looking at NFPA 13R, 2019 ed. it states:
6.6.6   Sprinklers  shall  not  be  required  in  attics, penthouse equipment  rooms,  elevator  machine  rooms,  concealed spaces dedicated  exclusively  to  and  containing  only dwelling  unit ventilation equipment, crawl spaces, floor/ceiling spaces, elevator  shafts....  and other concealed spaces that are not intended for living purposes or storage and do not contain fuel-fired equipment.

This would tell me that sprinklers are required due to the presence of fuel fired equipment, in this case a furnace.

However, section 6.6.6.1 says, When fuel-fired equipment is present, at least one quick-response  intermediate temperature sprinkler shall be installed above the equipment.

Then section 6.6.6.3 states, Where the fuel-fired equipment is above all occupied areas, sprinkler  protection shall not be required in the concealed space.

So, it seems to me that sprinklers will not be required since the furnace is in that attic and above all occupied areas.

Does this sound correct?

--

/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT

--