Correct, I single head above the equipment is required.



Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
*C:* 253.225.9977 | *E:* [email protected] | www.WC-3.com
<https://www.wc-3.com/>
*Teaming With Your Community to Make a Difference*


On Wed, Mar 11, 2026 at 2:43 PM Bob Knight <[email protected]> wrote:

> I'm a bit confused on whether sprinklers are required or not in an attic
> with fuel fired equipment.
>
> Looking at NFPA 13R, 2019 ed. it states:
> 6.6.6   Sprinklers  shall  not  be  required  in  attics,  penthouse
> equipment  rooms,  elevator  machine  rooms,  concealed  spaces dedicated
> exclusively  to  and  containing  only  dwelling  unit
> ventilation equipment, crawl spaces, floor/ceiling spaces, elevator
> shafts....  and other concealed spaces that are not intended for living
> purposes or storage and do not contain fuel-fired equipment.
>
> This would tell me that sprinklers are required due to the presence of
> fuel fired equipment, in this case a furnace.
>
> However, section 6.6.6.1 says, When fuel-fired equipment is present, at
> least one quick-response  intermediate temperature sprinkler shall be
> installed above the equipment.
>
> Then section 6.6.6.3 states, Where the fuel-fired equipment is above all
> occupied areas, sprinkler  protection shall not be required in the
> concealed space.
>
> So, it seems to me that sprinklers will not be required since the furnace
> is in that attic and above all occupied areas.
>
> Does this sound correct?
>
> --
>
>
> *Thank you, Bob Knight, CET III*
> *Fire by Knight, LLC*
> *208-318-3057*
> [image: FIREBYKNIGHT]
>
>
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> Virus-free.www.avg.com
> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> <#m_-2050872859198429910_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to