Yes, forgive me. I was thinking of CA requirements. Yes. it is required in
the crawl space not in the attic.




Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
*C:* 253.225.9977 | *E:* [email protected] | www.WC-3.com
<https://www.wc-3.com/>
*Teaming With Your Community to Make a Difference*


On Wed, Mar 11, 2026 at 3:35 PM Bob Knight <[email protected]> wrote:

> Craig,
> 6.6.6.2  states that, Spaces that contain fuel-fired equipment shall also
> comply with 6.6.6.3 or 6.6.6.4.
> Section 6.6.6.3 states, Where the fuel-fired equipment is above all
> occupied areas, sprinkler  protection shall not be required in the
> concealed space.
>
> The fact that the furnace is above all occupied areas would then allow for
> the sprinkler to be omitted, wouldn't it?
>
>
>
> *Thank you, Bob Knight, CET III*
> *Fire by Knight, LLC*
> *208-318-3057*
> [image: FIREBYKNIGHT]
>
> On 3/11/2026 2:52 PM, Craig Hanson wrote:
>
> Correct, I single head above the equipment is required.
>
>
>
>
>
> Craig D. Hanson, CFPS
> Fire Division Manager
> West Coast Code Consultants, Inc. (WC³)
> Meridian Satellite Office
> *C:* 253.225.9977 | *E:* [email protected] | www.WC-3.com
> <https://www.wc-3.com/>
> *Teaming With Your Community to Make a Difference*
>
>
> On Wed, Mar 11, 2026 at 2:43 PM Bob Knight <[email protected]> wrote:
>
>> I'm a bit confused on whether sprinklers are required or not in an attic
>> with fuel fired equipment.
>>
>> Looking at NFPA 13R, 2019 ed. it states:
>> 6.6.6   Sprinklers  shall  not  be  required  in  attics,  penthouse
>> equipment  rooms,  elevator  machine  rooms,  concealed  spaces dedicated
>> exclusively  to  and  containing  only  dwelling  unit
>> ventilation equipment, crawl spaces, floor/ceiling spaces, elevator
>> shafts....  and other concealed spaces that are not intended for living
>> purposes or storage and do not contain fuel-fired equipment.
>>
>> This would tell me that sprinklers are required due to the presence of
>> fuel fired equipment, in this case a furnace.
>>
>> However, section 6.6.6.1 says, When fuel-fired equipment is present, at
>> least one quick-response  intermediate temperature sprinkler shall be
>> installed above the equipment.
>>
>> Then section 6.6.6.3 states, Where the fuel-fired equipment is above all
>> occupied areas, sprinkler  protection shall not be required in the
>> concealed space.
>>
>> So, it seems to me that sprinklers will not be required since the furnace
>> is in that attic and above all occupied areas.
>>
>> Does this sound correct?
>>
>> --
>>
>>
>> *Thank you, Bob Knight, CET III*
>> *Fire by Knight, LLC*
>> *208-318-3057*
>> [image: FIREBYKNIGHT]
>>
>>
>> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>> Virus-free.www.avg.com
>> <http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>> <#m_5907575611153155660_m_-2050872859198429910_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing 
> list:https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to