I've pitoted main drains before, but never an Inspector's Test Connection
On Wednesday, March 11, 2026 at 08:55:25 PM EDT, [email protected]
<[email protected]> wrote:
Brilliant SL
From: Steve Leyton <[email protected]>
Sent: March 11, 2026 12:53 PM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]>
Subject: [Sprinklerforum] Re: inspector test connection
Todd:
I hate to pick nits here, but that’s a very selfish request. Why didn’t you
ask to have the test video-recorded so we ALL can watch?
For the good of the order, of course.
SL
From: Fpdcdesign <[email protected]>
Sent: Wednesday, March 11, 2026 4:34 AM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]>
Subject: [Sprinklerforum] Re: inspector test connection
The intent of the ITC is to simulate the flow of one sprinkler in order to test
the alarm activation. The fire pump has nothing to do with it. There is no
measuring the flow from it. However, if you colleague is going to pitot an ITC,
call me. I want to watch.
Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559
On Mar 11, 2026 at 5:54 AM, <Teaster1974> wrote:
I have a colleague that says must use fire pump rated pressure to determine
flow from inspector’s test connection. I said its a restricted orifice to
represent a sprinkler head flowing. Therefore pump pressure is negligible. Who
is right?
_________________________________________________________ SprinklerForum
mailing list:
https://url.avanan.click/v2/r01/___https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzo3NzMzYjA1YzAxMjdiYWUwZjI5ZTg0N2U3ZGU4MTAzNTo3OjUxY2Y6YjA2NTAyYWJlYTMyYTIyZjkzZWQ2N2IxM2VmNzViOGJjZTFhOWEzYzJlNWQ5MzhlNGY5ZmI4OTA2OTZlNzAxODp0OlQ6Rg
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]