American Fire Sprinkler Association
9696 Skillman, #300 Dallas, Texas 75243
Ph: (214) 349-5965        Fax: (214) 343-8898

-----------------------------
TECHNICAL UPDATE
DECEMBER 8, 2006
-----------------------------

"Are the seismic provisions in NFPA 13: 9.3.5 intended to be applied in 13R applications utilizing CPVC piping, particularly where no rods are used for hangers. Approved strap type Hangers and fasteners are used for CPVC piping?"

We have reviewed the 2002 edition of NFPA 13R as the applicable standard. Our informal interpretation is that it is necessary to apply the sway brace requirements.

Piping support is required by section 6.6.6 of NFPA 13R and shall comply with NFPA 13. There are no exemptions for sway bracing in the lateral and longitudinal directions provided for CPVC piping in the model codes. The manufacturer's data sheets also indicate the systems to be braced according to NFPA 13. Therefore, sway braces should be applied to the sprinkler system. It is reasonable to equate the strap type fasteners to hanger rods less than 6 inches as being able to adequately control horizontal movement perpendicular to the main. This allowance to act as a lateral sway brace is identified by 13:9.3.5.3.7. There is no similar allowance for short rods to act as a longitudinal brace because it cannot resist the horizontal force parallel to the main. The issue here is that the brace must be tightly fastened to the pipe in order to resist movement. Obviously a swivel ring with a short rod would not do this. Although the strap might be tight enough, there is a structural limit of the CPVC to resist compression when trying to ensure the brace is adequately tight. This is reflected by the fact that there are no listed longitudinal sway braces. There are only listed lateral sway braces which must be attached as an offset lateral brace acting as a longitudinal brace as discussed under 13:9.3.5.3.5. As such, you must use listed sway braces for this function.

------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2006, American Fire Sprinkler Association. All Rights Reserved
--------------------------