American Fire Sprinkler Association
9696 Skillman #300 Dallas, Texas 75243
Ph: (214) 349-5965       Fax: (214) 343-8898

------------------------------
TECHNICAL UPDATE
DECEMBER 14, 2006
------------------------------

"IS IT ALLOWED BY NFPA 13R AND NFPA 13D TO USE HAVE A 2-INCH OR SMALLER BALL VALVE AS THE SYSTEM CONTROL VALVE OR DOES THE VALVE HAVE TO BE OF THE SLOW-CLOSING TYPE?"

We have reviewed the 2007 Edition of NFPA 13R as the applicable Standard. Our informal interpretation is that the Ball Valve on a 2- inch and smaller Backflow Assembly does not have to meet the 5-second closure requirement. The 2-inch and smaller valve can also be the system control valve.

The issue of not being able to obtain a small listed backflow prevention valve that did not have ball valves was discussed by the NFPA 13R and D committee. The removal and replacement of the manufacturer's supplied ball valves with slower closing valves would void the listing of the backflow assembly. The committee also realized that the quick closing of a valve that was 2-inches or smaller would not produce a water hammer, which is a concern for larger valves. As a result, NFPA 13R: 6.7.1.5 now states: "System control or shutoff valves on backflow prevention devices that are 2 in. or less in nominal size shall not be required to comply with 6.7.1.4." The Subsection 6.7.1.4 sets the requirement that system control or shutoff valves be of the slow-closing type. It had been the committee's intent to restrict the use of the 2-inch and smaller valves in the past. Another improvement in the section on valves was 6.7.1.6, which allows a listed backflow prevention assembly to be considered a check valve, and an additional check valve shall not be required. NFPA 13 D: A.3.3.10.2 list "Ball Valves" as an acceptable control valve.

------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2006, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to (888) 839-4830 or e-mail @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.


_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to