American Fire Sprinkler Association
12750 Merit Dr., Suite 350 Dallas, TX 75251
Ph: (214) 349-5965       Fax: (214) 276-0908

---------------------
TECHNICAL UPDATE
MAY 2, 2007
---------------------

"I have an office building with a roof construction of plywood on metal trusses. The underside of the plywood decking will be completely covered with non-combustible batt insulation. The plywood is not fire-rated. The attic is separated from the space below by gypsum board attached to the bottom of the trusses. The attic is inaccessible. Since the plywood will be completely covered by the insulation, is it considered exposed? Is the attic required to be protected by sprinklers? If sprinklers are required, can the system in the attic be wet? The attic space does contain ductwork for heating the occupied space below the ceiling."

We have reviewed the 2002 Edition of NFPA 13 that you have identified as the applicable Standard. Our informal interpretation is that attic space as you have described it will not require sprinkler protection.

The attic space as you have described it meets the requirements of NFPA 13:8.14.1.2.1 for the omission of sprinkler protection. The plywood decking on the top of the roof joist is not an exposed combustible construction due to the insulation completely covering the underside surface of the plywood deck. If the insulation has a paper backing facing the concealed space, it must meet the requirement of 8.14.1.12 and not exceed a combustible rating of 1000 BTU per square ft. The attic space that has to be looked at would be that from the bottom side of the insulation to the topside of the gypsum board ceiling. This space is considered non-combustible. The space can contain ducts but cannot contain any fuel-fired equipment to maintain a non-sprinklered concealed space.

As to your question on using a wet system in this space if it had been required to provide sprinklers. The space would have to be maintained at or above 40 degrees Fahrenheit for wet sprinkler protection to be used.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.