American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph:(214) 349-5965       Fax:(214) 276-0908

-------------------------------
TECHNICAL UPDATE
May 16, 2007
-------------------------------

"Are sprinklers required under temporary seasonal marketing displays over 4 ft in width in department stores? Combustible materials (clothing, furniture, etc...) will be stored under displays such as canopies and umbrellas." We have reviewed NFPA 13, 2002 and 2007 editions that you indicated as the applicable standards. Our informal interpretation is that sprinklers are not required under obstructions that are not fixed in place.

Retail locations typically have displays that are assembled on a seasonal or promotional basis. Sporting goods stores or retail locations may also have outdoor furniture with umbrellas or even full size tents or canopies assembled for display. These items can be well over 4 ft wide and create an obstruction to the sprinkler discharge. Some fabric materials may be resistant to fire and others will burn away quickly. The other concern is that when these items are displayed, more surface area is exposed and may increase the intensity of the fire. However, these items are moveable and rather impractical to provide sprinkler protection under the obstructions. Section 8.5.5.3.2 states, "Sprinklers shall not be required under obstructions that are not fixed in place such as conference tables." The handbook commentary indicates that conference tables are likely to be moved and are not likely to have any significant combustibles located beneath them. An umbrella with outdoor furniture displayed under it would not be considered significant combustibles. However, a seasonal or promotional retail display of plastic items up to 6 to 8 feet with an obstruction over 4 ft wide could create quite a different impact.

Unfortunately, this becomes a policing event by the local AHJ. A canopy or obstruction that is fixed in place that creates an obstruction over 4 ft wide will require sprinklers. In addition, the retail location may construct temporary structures such as storage sheds or other structures to display items. Structures that create an obstruction over 4 ft wide will also require sprinklers. However, such items can be tolerated when the system is designed as extra hazard (Group II) for occupancies where shielding of combustibles is extensive.

-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to