American Fire Sprinkler Association
12750 Merit Drive, Suite 350 - Dallas, Texas 75251
Ph: (214) 349-5965       Fax: (214 276-0908

----------------
Tech Talk
May 2007
----------------

SMALL ORIFICE SPRINKLERS IN ORDINARY HAZARD OCCUPANCIES

Can sprinklers with a 4.2 K-factor in Ordinary Hazard (Group 1) occupancies be used? The answer is no since small orifice sprinklers are limited to light hazard occupancies.

Section 8.3.4.1 in the 2007 and 2002 editions state, "For light hazard occupancies not requiring as much water as is discharged by a sprinkler with a nominal K-factor of 5.6 operating at 7 psi, sprinklers having a smaller orifice shall be permitted..." The handbook commentary for the two editions indicate that small orifice sprinklers are restricted to light hazard occupancies because they are not as effective in controlling a fire as are sprinklers with a nominal K-factor of at least 5.6. Section 22.4.4.8.2 of NFPA 13 allows smaller orifices to be used, but also limited to light hazard applications. Section 22.4.4.8.2 states, "Sprinklers with differing orifice sizes shall be acceptable for special use such as exposure protection, small rooms or enclosures, or directional discharge. (See 3.3.15 for definition of small rooms and 3.3.20 in the 2002 edition.)" When looking at the definition of small rooms, it references light hazard occupancies. Once again, the wording is similar for the 2002 in section 14.4.4.6.2. The commentary also indicates that the exception does recognize that certain arrangements can require a reduced sprinkler discharge, thus a sprinkler with a smaller orifice is permitted. However, since the application is Ordinary Hazard (Group I) Occupancies, the use of a smaller orifice cannot be used.

COMBUSTIBLE CONCEALED SPACE WITH INSULATION

The technical committee cleaned up some language concerning the use of insulation in section 8.15.1.2.13 (8.14.1.2.13 in the 2002 edition). In addition, the substrate and facing of the insulation should also be considered. Section 8.15.1.2.13 was modified in the 2007 edition that states, "Concealed spaces below insulation that is laid directly on top of or within wood joists or composite wood joists used as ceiling joists in an otherwise sprinklered concealed space, with the ceiling attached directly to the bottom of the joists, shall not require sprinkler protection." This section now indicates that the composite wood joists can be the ceiling joists and that the ceiling is attached directly to the joists. This indicates that there is a very small gap below the insulation where sprinkler protection is not required.

The poly sheeting or paper facing of the insulation can impact concealed spaces. Insulation installed in a noncombustible concealed space may create a combustible concealed space due to the facing on the insulation. Section 8.15.1.2.12 previously required that the concealed space between the poly sheeting or paper and the suspended ceiling to be protected if the heat content of the poly sheeting or paper exceeds 1000 BTU/ft_. To ensure no misunderstandings, this was repeated within the new 8.15.1.2.16. You will have to confirm this with the manufacturer of the insulation when the poly sheeting and paper is attached to the insulation.

++++++++++++++++++++
Mark your calendars for the next Virtual Seminar
NICET TESTING PREPARATION - STUDY MATERIALS FOR INSPECTION & TESTING
May 30, 2007

12:00 PM Eastern
11:00 AM Central
10:00 AM Mountain
 9:00 AM Pacific

Earn:  0.15 CEU's  / 1.5 CPD's.
To Register:
Event ID: 12513
Member: $70 per connection Non Member: $100 per connection CEU Certificate: $40 per listener to receive CEU Certificate
By Phone: 800-676-0734, please have your credit card information ready.
By Fax: 800-775-0754 Fax completed form with Credit Card information.
By Mail: KRM Information Services Inc. PO Box 1187 Eau Claire, WI 54702-1187 (Payment must accompany registration)
Online: www.krm.com/afsa

Upcoming AFSA Virtual Seminars
HOW MUCH IS MY COMPANY WORTH?
June 20, 2007
To Register:
Event ID: 12513
For more details go to: http://www.krm.com/afsa

COMMISSIONING
July 11, 2007
To Register:
Event ID: 12911
For more details go to: http://www.krm.com/afsa

2007 AFSA Design Schools
BEGINNING SYSTEM PLANNING SCHOOL
July 9-20, 2007 Sold Out!
August 6-17, 2007 Sold Out!
October 8-19, 2007
November 5-16, 2007
December 3-14, 2007
Registration Prices:
        Member  $1200
   Non-Member   $1700

++++++++++++++++++++++
TechTalk is prepared by the Technical Services Department of the American Fire Sprinkler Association: Vice President of Engineering and Technical Services, Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a CFPS and a NICET IV certified automatic sprinkler technician, and Tom Wellen, a degreed fire protection-engineering technologist. Opinions are provided with the understanding that AFSA assumes no liability for the opinions or actions taken on them and they are not to be considered the official interpretation of the NFPA or that of its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association, 9696 Skillman St., Suite 300, Dallas, TX 75243. Voice (214) 349-5965 ext 124 or Fax (214) 343-8898. All rights reserved.

++++++++++++++++++++
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to