"We have installed new drops off of existing branchlines for coverage below a new suspended ceiling. We cannot isolate the drops for hydrostatic testing. Does 24.2.1.6 apply to new drops and is there any limit to the number of drops that this section applies to?"

We have reviewed the 2007 Edition of the NFPA 13 that you have identified as the applicable Code or Standard. Our informal interpretation is that Section 24.2.1.6 does apply to your situation and that Section 24.2.1.6 does not set a limit on the number of relocated drops.

The requirements of Section 24.2.1.6 often gets confused with the isolation and testing requirements of Section 24.2.1.5 that requires isolation and hydrostatic testing when a system modification consist of 20 or more sprinklers. As explained in the Automatic Sprinkler System Handbook, "When new portions of a system cannot be isolated, such as relocated drops, NFPA 13 provides some flexibility and permits hydrostatic test to be conducted at the system's normal static pressure". This relieves the requirement to subject the existing portions of the system from a new hydrostatic test of 200 psi for 2 hours.

When it comes to items such as relocated drops or new drops being installed to a sprinkler, NFPA 13 does not set a limitation to the number of drops involved. You can have one or you could have hundreds. However if modifying a portion of the system, including a modification to branchlines and/or cross-mains as well as drops, that consist of 20 or more sprinklers, isolation of that portion of the system is required with a minimum hydrostatic test at 200 psi for 2 hours.

--------------------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.

Copyright (c) 2007, American Fire Sprinkler Association. All Rights Reserved
--------------------------
If you'd rather not receive future faxes from AFSA, fax your removal request to Linda Dawson at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful. _______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to