A ceiling cloud obstruction attached to a wall is provided over an entry door that measures 15 ft by 3 ft 11 in. When the measurement is taken from the doorjamb, the distance is 4 ft 1 in. where the AHJ is requiring a sprinkler under the cloud. Do we measure the width of the obstruction from the wall or the door jamb?



We have reviewed 13, 2007 Edition as the applicable standard. Our informal interpretation is that when architectural features such as windows and doors create additional floor area, the distance is measured to the door or window surface.



This issue was clarified in the 2007 Edition in Section 8.5.3.2.4 where it states, "The distance from the wall to the sprinkler shall be measured to the wall when sprinklers are spaced near windows and no additional floor space is created." Since the door jamb creates an additional floor space, the distance is measured from the side of the obstruction (ceiling cloud) to the side of the door jamb. Thus an additional sprinkler is required by Section 8.5.5.3.1 since the obstruction width is greater than 4 ft. This is supported by the NFPA 13 Handbook text that states, Paragraph 8.5.3.2.4 applies when the wall is represented by a window. Where the window in the wall is set back from the inside surface of the wall, the distance is measured to the wall, and not to the glass surface of the window where no additional floor area is created by the window. Where additional floor area is created by the window, the distance is measured to the glass surface of the window.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright ⌐ 2008, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you'd rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [EMAIL PROTECTED] Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful._______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to