American Fire Sprinkler Association

12750 Merit Dr., Suite 350,  Dallas TX 75251

Ph: (214) 349-5965   Fax: (214) 276-0908



----------------------------------

TECHNICAL UPDATE

FEBRUARY 4, 2009

----------------------------------



“Does the presence of the fuel fired equipment (gas fired water heaters) in an otherwise unused attic as referenced in NFPA 13R, Section 6.9.6 require the attic to be designed and calculated for other than light hazard occupancy?”



We have reviewed NFPA 13R, 2007 Edition that you indicated as the applicable standard. Our informal interpretation is that the attic space will have to be protected to the spacing and hydraulic design criteria of NFPA 13 for Light Hazard Occupancies.



NFPA 13R Section 6.9.6 will require the protection of attics that contain fuel-fired equipment. The design criteria for the attic are set by 6.8.2.1 that directs you to NFPA 13 and it states, “For areas outside the dwelling unit, the design discharge and design area criteria shall comply with NFPA 13, Standard for the Installation of Sprinkler Systems, unless permitted by 6.8.2.2 and 6.8.2.3." This clarifies that the requirement for the protection of the attic will have to be to NFPA 13 requirements. The area will have to be designed to light hazard occupancy if it does not meet any of the allowances of NFPA 13R, Section 6.8.2.2 and will have to be a minimum of 1500 sq. ft with a density of .10 gpm/sq. ft. Regular mechanical rooms in NFPA 13 occupancy with gas-fired equipment are typically ordinary hazard occupancy. Two primary reasons are that the equipment is typically large and we expect the owner to use the space for storage and collected combustibles. Mechanical rooms without gas-fired equipment typically get kicked into an ordinary hazard classification for the later reason. In this case of water heaters in an attic, not only are the units small, it does not add to the fuel load but it is an ignition source. Thus, the definition for light hazard “where quantity and/or combustibility of contents is low” does apply.



-----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright © 2009, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you’d rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [email protected]. Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.