American Fire Sprinkler Association

12750 Merit Dr., Suite 350 * Dallas TX 75251

Ph:  (214) 349-5965   Fax:  (214) 276-0908





----------------------------------

TECHNICAL UPDATE

FEBRUARY 18, 2009

----------------------------------



How do you approach a hydraulic remote design area where the branch line is of insufficient distance to meet the 1.2 length?



We have reviewed NFPA 13, 2007 Edition as the applicable standard. Our informal interpretation is that there are two basic requirements in establishing the design area configuration. The first size is 1500 sq. ft., etc., and the other is 1.2 times the selected design area to establish a rectangular design area. The base requirement is that the design area must be met.



Section 22.4.4.1.1.3 explains how to address deign areas where the branch lines are not long enough to satisfy the 1.2 requirement. As an example, lets consider a building that is 39 feet wide and 100 feet long with purlins running perpendicular to the 39-foot dimension. The head spacing on the branch lines are at 13 ft on center and 10 ft on center between the lines on a side-feed crossmain. There will be 3 heads on each branch line. The selected design area is 1500 sq. ft. The requirement of 1.2 times the square root of 1500 results in 46.48 ft that cannot be met. The design area of 1500 sq. ft. still must be met which will require going down the crossmain picking up additional branch lines. This will require traveling a minimum of 38.46 ft (1500 divided by 39) which in this scenario will require five branch lines. An example of this scenario is given in Figure A.22.4.4.1 (a) System D.





----------------

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire protection engineering technologist. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees.



Copyright ⌐ 2009, American Fire Sprinkler Association. All Rights Reserved

--------------------------

If you╒d rather not receive future faxes from AFSA, fax your removal request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send e-mail request @ [email protected]. Please include your company name and the specific fax numbers(s) at which you do not wish to receive faxes from us. Our failure to comply with your request may be unlawful.