American Fire Sprinkler Association
12750 Merit Dr., Suite 350 * Dallas TX 75251
Ph: (214) 349-5965        Fax: (214) 276-0908

---------------------------
TECHNICAL UPDATE
JUNE 25, 2009
---------------------------

“We have a hospital that has a single water supply coming into the  
building and 6 vertical Class I standpipes with no fire pump.  The  
height of the building varies between 4 and 7 stories. They want to  
comply with NFPA 25 requirement to have a flow test performed every  
five years on their standpipe system. NFPA 25 indicated that a flow  
test shall be conducted every 5-years at the hydraulically most remote  
hose connection of each zone of an automatic standpipe system to  
verify the water supply still provides the design pressure at the  
required flow.  NFPA 14 indicates a standpipe system zone is a  
vertical subdivision of a standpipe system by height. Are we to test  
the 2 1/2 in. hose valve on each floor for the most remote standpipe,  
only the most remote 2 1/2 in. hose valve on the top floor of the most  
remote standpipe, the most remote hose valve of each standpipe riser  
or some other combination? What is the intent on NFPA 25 for flow  
testing standpipe systems?”

We have reviewed NFPA 25, 2008 Edition as the applicable standard.   
Our informal interpretation is that a 5-year flow test is to verify  
the water supply still provides the design pressure at the required  
flow for automatic standpipe systems.

The 2002 edition of NFPA 25 referenced testing the most remote hose  
connection.  This has been misinterpreted by many to mean that the  
flow for only a single connection needs to be tested (which logic will  
not support since everyone knows the water supply adequacy relates to  
the system demand). The intent was clarified by the 2008 edition.  
Section 6.3.1.1 now states for flow tests, “A flow test shall be  
conducted every 5 years at the hydraulically most remote hose  
connections of each zone of an automatic standpipe system to verify  
the water supply still provides the design pressure at the required  
flow.” The words to stress in this section are “automatic standpipe  
system” since the flow test is only required for automatic systems.  
NFPA 14's definition of an automatic standpipe system is a standpipe  
systems that is attached to a water supply capable of supplying the  
system demand at all times and that requires no action other than  
opening a hose valve to provide water at hose connections.  The  
standpipe system has to be flow tested for hydraulically calculated or  
pipe schedule designs and only if an automatic water supply is  
provided. The NFPA 25 Handbook indicates that the flow test is based  
on the calculated flow of 500 gpm for the most demanding riser and 250  
gpm for each additional riser up to a maximum of 1250 gpm for  
buildings that are partially sprinklered and 1000 gpm for buildings  
that are fully sprinklered. As addressed by proposal 14-71 (ROP for  
next cycle), you perform two separate tests. One is for all the  
standpipes on the single highest floor to account for maximum  
elevation (assuming there are only two standpipes available). Then do  
a second test of the standpipes at the next highest story that allows  
the maximum flow, i.e. 1,250 gpm or 1,000 gpm when sprinklered on one  
level. So if the highest level that has four standpipes is on the 4th  
story that is where you do the second test. This is based on manual  
fire fighting being applicable to a single fire area.
-----------------
Technical Update is prepared by the Technical Services Dept. of the  
AFSA: Vice President of Engineering and Technical Services Roland  
Huggins, a PE registered in fire protection engineering; Phill Brown,  
a NICET IV certified automatic sprinkler technician and NFPA Certified  
Fire Protection Specialist (CFPS) and Tom Wellen, a degreed fire  
protection engineering technologist. This is provided with the  
understanding that the AFSA assumes no liability for this opinion or  
actions taken on it and they are not to be considered the official  
position of the NFPA or its technical committees.

Copyright © 2009, American Fire Sprinkler Association. All Rights  
Reserved
--------------------------
If you’d rather not receive future faxes from AFSA, fax your removal  
request to Amy Sweeney at Efax (214) 242-3155 or call toll free (888)  
839-4830 or send e-mail request @ [email protected]. Please  
include your company name and the specific fax numbers(s) at which you  
do not wish to receive faxes from us.  Our failure to comply with your  
request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to