TECHNICAL UPDATE
JANUARY 27, 2010
-----------------

2010 Beginning System Planning School
February 22-March 5, 2010 
Register Now. Openings still available.
Registration:  Special Member $880       Non-Member $1600

********************************************************************************

“NFPA 13 in the 2007 Edition in Section 8.15.7.3 states, sprinklers shall be 
permitted to be omitted from below the canopies, roofs, porte-cocheres, 
balconies, decks, or similar projections of combustible construction, provided 
the exposed finish material on the roofs, canopies, or porte-cocheres are 
noncombustible, limited-combustible, or fire retardant-treated wood. Does the 
noncombustible, limited-combustible statement refer to all the exposed surfaces 
including the roof? My interpretation is that 8.15.7.3 is only referring to the 
area below the canopy, roof, or porte-cocheres and that the noncombustible, 
limited-combustible requirement is aimed toward the ceiling and wall finish of 
the area below the canopy not the roof decking and overlay.”

We have reviewed NFPA 13, 2007 Edition that you indicated as the applicable 
standard.  Our informal interpretation is that noncombustible, 
limited-combustible statement refers to the all exposed surfaces including the 
roof membrane.

In Section 8.15.7.3, sprinklers may be omitted from a combustible roof, canopy, 
or porte-cochere where the exterior surfaces are of noncombustible, 
limited-combustible, or fire-retardant treated wood as defined in NFPA 703. 
Thus, the TPO (Thermoplastic Olefin) roof membrane cannot be combustible. The 
committee placed the requirement on the exterior surfaces including the roof so 
that the fire would not wrap around and start the roofing material on fire. 
Some manufacturers of the material may treat the membrane to have fire 
retardant properties where it will not sustain combustion. The membrane 
apparently meets the Standard Test Methods for Fire Tests of Roof Coverings, UL 
790. Under the scope of this standard, it states, “1.1 These requirements cover 
the fire resistance performance of roof coverings exposed to simulated fire 
sources originating from outside a building on which the coverings are 
installed.  They are applicable to roof coverings intended for installation on 
either combustible or noncombustible decks (see 1.7) when the roof coverings 
are applied as intended. 1.3 Class A roof coverings are effective against 
severe fire test exposures. Under such exposures, roof coverings of this class 
afford a high degree of fire protection to the roof deck, do not slip from 
position, and are not expected to produce flying brands.” The membrane is 
reported to be Class A. This meets the intent of Section 8.15.7.3 to omit 
sprinklers. Another construction feature shown on a diagram that you provided 
is the membrane is installed over Densdeck Prime cover board. The 
manufacturer?s information for this material indicates that the Densdeck can be 
used as a fire barrier over steel decks and combustible roof decks. In 
addition, the area of the application is approximately 460 square feet and is 
used to cover a pedestrian walkway. A fuel load such as a burning vehicle is 
not expected under this canopy since it is a pedestrian walkway so the fire 
risk appears to be low.
-----------------
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a degreed fire protection engineering technologist.  This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. 

 Copyright ? 2010, American Fire Sprinkler Association.  All Rights Reserved
--------------------------
If you?d rather not receive future faxes from AFSA, fax your removal request to 
Amy Sweeney at Efax (214) 242-3155 or call toll free (888) 839-4830 or send 
e-mail request @ [email protected].   Please include your company name 
and the specific fax numbers(s) at which you do not wish to receive faxes from 
us.  Our failure to comply with your request may be unlawful.

_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to