Having trouble viewing this email
click here
http://campaign.r20.constantcontact.com/render?ca=014203ca-97a8-4db5-b5ae-5dfc6b668123&c=9f129e90-caf6-11e3-83cb-d4ae5284205e&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A weekly newsletter dealing with codes and other technical issues

April 27, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Control Mode Density-Area Sprinklers

"When applying Control Mode Density-Area (CMDA) design per Table 18.4(b), do you
 have to use sprinklers that are specifically listed as CMDA?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that the phrase control mode density-area sprinkler refers to
 the standard spray sprinkler used for protecting storage applications.

The use of standard spray sprinklers for storage applications has been applied 
for
quite some time.  The use of the term "control mode density-area" may not be 
indicated
on the manufacturer's data sheet and does not disqualify its use.  There will be
 a definition added to the 2016 edition as follows: 3.6.4.1* Control Mode 
Density/Area
(CMDA) Sprinkler.  A type of spray sprinkler intended to provide fire control in
 storage applications using the design density/area criteria described in this 
standard.
 With that said, NFPA 13 requires the use of listed storage sprinklers for 
higher
densities.  Lower densities use a regular standard spray sprinkler.  Section 
12.6.3
indicates for general storage applications, rack storage, rubber tire storage, 
roll
paper storage, and baled cotton storage being protected with upright and pendent
 spray sprinklers with required densities greater than 0.34 gpm/sq. ft., 
standard
response spray sprinklers with a K-factor of K-11.2 or larger that are listed 
for
storage applications shall be used.  There is an exception to this for existing 
systems.  Section 12.6.4 indicates that unless the requirements of 12.6.5 are 
met,
the requirements of 12.6.2 and 12.6.3 shall not apply to modifications to 
existing
storage application systems, using sprinklers with K-factors of K-8.0 or less.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Open for Public Comments

The first draft report for the next edition of NFPA 25, Standard for the 
Inspection,
Testing, and Maintenance of Water-Based Fire Protection Systems, is open for 
public
comments.

Public Comment Closing Date for Online Submission: 5/15/2015

Public Comment Closing Date for Paper Submittal: 4/10/2015

http://www.nfpa.org/25 [http://www.nfpa.org/25]

2017 edition:

Posted under Next Edition tab:
First Draft Report - open for public comment 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AqbWoHLlKOnFkI93LAUaBzPM4RGnp8IrgKqi-oWKRAFWrnnk67WL3kaCnrk8tBkNmNDnzO3Yx84Ezfy25e7jDSNvItj5zBw4wUmyNE2USSo2rVNq1gsY6L8Kox9SMaF9LHwp9YLgASRKqUsmTSTZcgyWO01sH6_wVTTBFDy6d0K9tqS618VYu3QaUhHhei7yrsL47K-i9kbW7gyGyStocAUGV0OoySUVkwtRP0ZNz9B4&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
First Draft Ballot Final 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AgjOauAmbNgZidhCUtxQJzDx7EVTlaWM24_mZi7y-XItqCgVCkdKIgbMpSdRX9642WNtrOTfT98VaNNFnuo1I6zc9o-B_8HcbSyGDBL3CDJ2Fao28aR5yIEo128ZtMB4Klu_xDPwZIRMfLBOth_7sr9EoZTQTsq4wd7yuu3gEUmg3s2CSxcnwdRlxCaMBJooE6lMdV68ni-1081lMfeGAjg=&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AlSY530av5JEcQqWGlZ9A0r7fdU0rkVD3DPFBNwzDzrKq1ZysOS8vgpQs--9vPcl-S7PU9SZW114nO8-GqLmyFAz11-_yLrEB2c5qpXlWm3rG4OUq63qnBXhXuCBUKjwMQ==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AmqGiDc7o7U4_gSXjCNSfcNBCymjZb_wSelB4Zron04YWJqrlM5oGmgHGSqj4ihNsiTutK37jrWj-UlzlsoBbk0rkgxJ9WXaROuhVH4zXaN-k94wHS7Alp5k9fAtzSiedg==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AmqGiDc7o7U4_gSXjCNSfcNBCymjZb_wSelB4Zron04YWJqrlM5oGmgHGSqj4ihNsiTutK37jrWj-UlzlsoBbk0rkgxJ9WXaROuhVH4zXaN-k94wHS7Alp5k9fAtzSiedg==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1Ai-AsM2et8y3KOYLY4hxKnG2WMQt70QZjoDVPh08cl3OUX0xrbcXmGoEh19_EZ9m56CrsaFlPyaVhlRQLVQ9-dUBiEgmMrWFhbVBfhufalEEmndHL4MixuWFUAxTwEl78tRFp_0I1rpfIw-QKmDCdNvgvq8nVyz7X__bGprDjp9wA9n8KEGQfH8=&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AtLa6dQE87IvmJz5FOnrZdB_aMYiGwwiy08fIEFBfgwMdEJyoTvYQpjRbfRWqaUdDrDGBVqQeq0nb5CuTFk7Q8agbMEp5memYHuVaS4wv51bPdISAmCLxxM0-f7JIAIHCxlTQzqGA-XG1IT6vggBrcwriz6yd51CHQ==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AtLa6dQE87IvQWhDKKLFiFk3L2F2P0xHQsHPdM4YrK7orDUYlKvhvg5RdyGIKX7h8DTSHVGJCNMMrib1Pi5x-P48G255ZF1PSJgAWOQPElWMkOPE1ZbNAt2an_7QaDiAxKfVrh1c7VpzhKXeY0p02TB0kwQrrb3zq66ODxN9IKy2KhuLS_uDZ6j82ku7iDjyZQ==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1ArQOAgpoHj_bIx8x9P2Fi5rC4pwYrS5lsFmWs7BCFgino-ac0ibCjoU8Y-PL-_OLJMrouJ5eyeHtRAiF9mSlxfrqUzjF43ZfBzeoTIIyLjqOl9hSc1a0dn-gVJ22P-2VxdRjxrZXytPl5DfSAXUU_pf0fjTDWfDov0zUG4ZXZq-BLCcYjEbZtwcmIweu2_dsSQ==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AhUg92ExPvlgUGw-9chuAQd71so2Y3tuwIvnMQgi5i4QDu_fOLnF_1hyJiQlaWonk2F5YtYwA7mPJrnCLV_BqU2g7gtBD0bIt9EUDQ6KSE0LrrtwU8PnUTgnfalvBXs_J2wMSI2S8op1V-WBa6m7W7nBbl8rx5RMH2ZRDTTkdla_3Lin265b5u6d9aydSx6Nxw==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1AhUg92ExPvlgNp0tvDfu8w_KtXNfW8kzABast91v2gjWu7zuU80eR5-PyL_B4GADNlpObK0eHg-1ux40QK5U2HLE7q5rt715MsstshihgaKDDCLxQDX_Tf9GbLRDUqo23ZKNbaTJbqgD&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
July 20 - 31, 2015
September 14 - 25
November 2 - 13
May 11 - 22, 2015
Sold Out!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001WssaxD7IsROgfm6gB177vbQM22BDp-RuHG_2rqs2GT7oA8XEbtd1Ajnldzsa2WRcTw2HTiN6UVJrRntrKrY2Wnm67GXkxP8NjXAP7x-tNXux-L6ZwHVS_hVRXSIP12Azm4GCsdifMhytu3tCnVGIDxTKN0zLmffeVb0fJKTICYNnlXXt9AqiMw==&c=QUmHitGkq2014oNNAwvOl40TkoxMem4IUwn0Qvraye9kJjqsBlYkbA==&ch=KC4ioK92FRW6oE3DGtbheNnwE0E537xWt0q0BTsWoyw1rnbiJ7tyrw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1120813785222

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=014203ca-97a8-4db5-b5ae-5dfc6b668123


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=014203ca-97a8-4db5-b5ae-5dfc6b668123


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to