December 7, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Intermediate Temperature Sprinklers in Conditioned Spaces
"We are designing an apartment complex per NFPA 13 requirements.  Is it 
permissible
to install intermediate temperature sprinklers throughout all spaces (except 
those
that would specifically require a high temp sprinkler due to other sections)? 
The
specific question arises because we have ordinary temperature sprinklers 
throughout
most areas, and intermediate temperature sprinklers in mechanical closets and 
laundry
rooms in the dwelling units.  The AHJ states that since the areas are 
conditioned
spaces, that we must use ordinary temperature rated sprinklers.  Is that 
correct?"
We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that intermediate temperature residential sprinklers can be 
installed
throughout the premises.
Historically, the base requirement per Section 8.3.2.1 was to use an ordinary 
temperature
rating throughout all buildings unless higher localized temperatures required a 
higher rating.  There was also the allowance to go to a high temperature rating 
for extra hazard occupancies and storage. This was changed in the 2010 edition 
whereby
one could also install sprinklers with an intermediate temperature rating 
throughout
all facilities.  This section says unless the requirements of 8.3.2.2, 8.3.2.3, 
8.3.2.4, or 8.3.2.5 are met, ordinary- and intermediate-temperature sprinklers 
shall
be used throughout buildings.  The substantiation for this change in the 2009 
Report
on Proposals in 13-125 Log #89 stated, "Many commercial facilities are omitting 
a drop ceiling (simply painting the upper area black) and often installing many 
HVAC diffusers.  This has lead to some cases where 1/3 of the sprinklers have an
 intermediate rating in order to satisfy Table 8.3.2.5(a).  With standard 
response
sprinklers a lower temperature rating makes sense.  Now that quick response 
sprinklers
are required, the difference in activation time between the two temperature 
ratings
is not significant but the impact on installation is significant."  The handbook
 commentary for this section says that traditionally, ordinary-temperature 
sprinklers
have been required throughout a building unless the requirements of 8.3.2 
required
intermediate- or high-temperature sprinklers to be used.  However, many 
buildings
are built without suspended ceilings, resulting in a mix of ordinary with the 
intermediate-temperature-rated
sprinklers needed around heating diffusers and other heat-producing areas.  
Since
the response time of quick-response intermediate-temperature sprinklers is not 
that
different from ordinary-temperature standard-response sprinklers, the standard 
now
groups ordinary- and intermediate-temperature sprinklers together and allows 
intermediate-temperature
sprinklers throughout the building, reducing the need for multiple types of 
sprinklers.
 Section 8.3.2.4 applies where sprinklers are installed in specific locations as
 required by 8.3.2.5.  The applicable portion for your installation would be 
Section
8.3.2.5(8).  Table 8.3.2.5(a) dictates the minimum temperature rating required 
near
heat producing devices.  It does not define the maximum rating. That is dictated
 by Section 8.3.2.5.
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsvUdNVaXADkBp_hmfgcUni9JwamEWGqJVQ6Zv0Xbw9AhXQ0D-EjLUD8iM-DABfPrl2vzxowxEdXWk2bSTyTrtJjtMI27Nft5byBP9SZOkdjV5ZPZvAueVhFg==&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsvC8PEpvIpNa5qcGRVELjMrGkJ1q2EHMyTiZAMy2pv7mQP-WvW4qVeJ7ZDPfRUM5iL2f54MqGZgmYtbq26SWwaO7_KqVwxDxLx_OB9zCZAewPbOBcRNI8zNRxv4V8wB9uYShinH2mKK34k9CSBLfckTXF2Y4UTerew&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsvt2PpLG_1l9enaIeOn_oFD5-RQIqwTKVtQ72lvIH8i9JcX_W2pU3SuLeMTAvsE_5bJjcB-IaRjsIxVsMj_ayqPNt-42qxcIj6jlrARPJSLvRNDOTufHmhww==&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsvtwMsDKHwssmpsm_J_FcKYOLzDf4eGDP8XQKgnhOEtAXHAHc3qJAVUGegcAXw1dnD698dPNlO9fUXBqtzWGedykgfTbVdngaVHvz2myCXP-hUmSZ4eLUuhXJ9lomtE5swI1vIODq5EZHSQ-HMPLSem7Tz2DWG5sYnbwlZQprtRjE=&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsv03V1TDsfkDKnxLK1zs911fjcppPo_Jt6o0yohhq7Kz5okminkizQuyuFvM0pAc7Slt6cHUxUog7w7ubw1-EOxhtwpoK67b6v6Hau7yk4jTxmre-TSG_r6ThAJlazc88j4Dym9Erit-40oi4W8o9AdQ==&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsvkhhXal58Ylnj4AbKdGCs3pD7rF31y_997pyWP-4SBXKkyaV8-Cpl7z-L1K1IVrNytFl9xEEBlk3e1azblNaJDGu0jTiuEeTlasNTanN5F8Syf-Ezu7PenU-yAD-hgPI7FosKcrnubxrXbhZ5kCdEhXJnWIs6XfAYR5f-3sytz-UhfyG4oNAIgzJyzA2Y6mW6RDTBxeKCZjgd9ybCpvOotLlJBf94CsBP&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning Fire Sprinkler System
Planning School
2016 Schedule
Jan. 11 - 22, 2016
Feb. 8 - 19, 2016
April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
For more info, call:
214-349-5965 ext. 132
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers
If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/ maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!
Click HERE  
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7GQFRO-yVBB4DiyWRPYBoMhFQG6lwZOhzKz5mroWQHtuG-thZvxAHi2AI-C1IihK5ZvTQXkIyH_rGjsThVIPq7PQXWSc2xINmYjVdLgiqZtyBpploXsoIckqVaPoTR8RwueYiYYztDQl&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]for
more details
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Link 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7K86QleVGk3DgSTeCbuCSHbHYqpek3VPR1cpd1zrXNMRkJ_6lNJRA51sGYRBGJ8_7ThiO06-6pT3xEg_uaVuhX8Y5LBVWHxvb0Z9JCwpLa2WTo7uA6Yxb1u2HBa_Yfy5xkrlDO6bOWCXzyhauW7GZYf4E3k98YqXJw_DvyK8odGD0boCUSA3mWFTa0CVOZLiGA==&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
Archives 
[https://www.firesprinkler.org/technical-services/subscribe-technical-updates/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001Iz5rLZPYU5fJ8OHFeDsGaIo5t5WQBJbGZA1Cm1xvAmblWkpJNr1w7F8PjfxAwIsvvad8QEPLKe-pBjoVJmUWTDIBDtsFGGnV3lswITXL4EihczvI7SFj5rzn_jr6DP7QDs1M8YRgKHPUCipNe7vLVBgbB7IHDJKX0Pp4qQxoeB4BmII1voeHqSZtMK_iTPZhBoWEMg7h_LYOiFDNdwjudEtmAkQpR02b8cWDxCaA20fnsNbIWb0b-77B2tsPIJYT&c=-BOoeR8haznVP6jWGBG5RZ9UL_X06wW1PdLDpFQhcGuWGGSHzeRhMQ==&ch=5FzMZnp501kOuIXIjvxooDh8G3aPBoek-NjQNJMolfl-GhoEPa8Czw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1123049812818

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=b3df5e61-4210-4bd3-b481-808adcc857aa


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=b3df5e61-4210-4bd3-b481-808adcc857aa


Privacy Policy:
http://www.constantcontact.com/legal/service-provider?cc=about-service-provider

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to