March 21, 2016

Sidewall Sprinkler Above Light Cove
 
"An architect wants to use a light cove in corridors of an NFPA 13R senior 
apartment project.  The sidewall deflector is 12 in. down from the ceiling and 
the body and escutcheon is even with the front of the light cove.  The width of 
the light cove is less than 8 in. and the bottom of the cove is approximately 
30 in. from the ceiling.  Do sidewall sprinklers located 6 in. from a wall 
above the light cove meet the intent of NFPA 13R?"
 
We have reviewed NFPA 13R, 2010 edition that you indicated as the applicable 
standard.  Our informal interpretation is that this arrangement should be 
allowed.
 
If the area above the light cove could be converted to a soffit, this 
arrangement would comply with section 6.4.6.3.6.2.  If modifications to the 
current arrangement are not possible, this should be permissible if allowed by 
the AHJ.  The NFPA 13R standard cannot address every possible sprinkler 
application, but there are clues that this arrangement should be allowed.  The 
basis for evaluating such equivalencies, although not stated in NFPA 13R is 
stated in NFPA 13, Section 8.1.1(3), is that sprinklers are located to provide 
satisfactory performance with respect to activation time and distribution.  
Lets first look at distribution.  Since the sprinkler is even with the front 
edge of the light cove (the same as it would be if a soffit was above the 
cove), the distribution is acceptable.  This leaves the question of whether it 
has an acceptable activation time.  It should noted that there is also an 
allowance whereby the sprinkler can be installed in the same wall above the 
cabinet provided that there is a clearance of at least 3 ft between the 
sprinkler and the top of the cabinet.  The 3 ft is needed to ensure the 
distribution is not excessively obstructed.  I mention it because it shows the 
sprinkler activation time is acceptable without a soffit above the cabinet.  
Actually, the activation time will likely be faster with your arrangement. This 
is because the sprinkler will be directly in the plume if the heat is flowing 
up from beneath the light cove and if flowing across the ceiling, the space 
above the light cove has a much smaller volume than the cabinet with a 3 ft 
clearance. As with all things not specifically addressed by the standard, 
obtain approval by the AHJ.


Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President of Engineering and Technical Services Roland Huggins, a PE registered 
in fire protection engineering; Phill Brown, a NICET IV certified automatic 
sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and 
Tom Wellen, a PE registered in fire protection engineering. This is provided 
with the understanding that the AFSA assumes no liability for this opinion or 
actions taken on it and they are not to be considered the official position of 
the NFPA or its technical committees. 

Copyright 2016, American Fire Sprinkler Association. All Rights Reserved


Training Calendar 

AFSA Beginning Fire Sprinkler System
Planning School
 
2016 Schedule

April 4 - 15, 2016
May 16 - 27, 2016
July 18 - 29, 2016
Oct. 3 - 14, 2016
 
For more info, call: 
214-349-5965 ext. 132


Reply via email to