Auditoriums and Water Supplies


You asked the following questions: “We have a 4-floor building with floor 
control valves in the stairwell. There are fire sprinklers in an auditorium 
that span from the 1st level to the 2nd level. The water is supplied from the 
2nd-floor level fire sprinkler piping as that is the level of the auditorium 
ceiling space. The Baltimore office is requiring the water be from the 
1st-floor level fire sprinklers as the sprinklers are ‘seen’ from that level 
when looking up. The Baltimore office tells me that the 1st-floor feed 
requirement is per NFPA 13. Is there such a requirement in any NFPA codes that 
the fire sprinkler water be supplied from the floor level that you ‘see’ the 
sprinklers?” In response to your question, we have reviewed the 2018 IBC, NFPA 
13, 2016, and NFPA 72, 2016 editions as the applicable standards. Our informal 
interpretation is this is a fire alarm issue.

Supplying a sprinkler system in this manner can create an issue for a fire 
department responding to a fire event. Since the system is supplied from the 
second-floor system riser and if a fire were to activate sprinklers in the 
auditorium, the alarm system would be notifying the fire department that a fire 
is located on the second floor and not the first-floor auditorium area delaying 
firefighting efforts. Historically, this arrangement would have been acceptable 
but since the advent of flow switches per floor, it now conflicts with the 
zoning requirement for the fire alarm system. Additionally, the IBC Section 
907.6.4 states: Each floor shall be zoned separately, and a zone shall not 
exceed 22,500 square feet. The length of any zone shall not exceed 300 feet 
(91,440 mm) in any direction. Technically, the auditorium is part of the first 
floor as that is where the access would be from even though the ceiling is at 
the same plane as the second-floor ceiling level.This section could be the 
driving factor in why the AHJ is making that requirement. Furthermore, NFPA 72 
Section 10.17.5.1 states: For the purpose of alarm annunciation, each floor of 
the building shall be considered as a separate zone for the very reasons 
explained above.