On Thu, 21 Aug 2008, Stuart Anderson wrote:
>
> FWIW, we are running S10U4 fully patched. To be pedantic, are you saying that
> you have 6140 arrays and that rebooting a machine on the SAN causes some of
> the volumes to be internally mapped in the 6140 to their non-preferred 
> controller?

It is a 2540 rather than a 6140.  I don't recall seeing this issue 
under S10U4.  For my case, since there is a volume per disk (expensive 
JBOD), the preferred configuration reaches six disks per fiber channel 
path and also via the preferred controller for those disks.  This 
optimum configuration allows 2-3X the performance that Sun admits to 
in their formal benchmark report for the 2540 (278,530KB/s write, 
522,930KB/s read).

I am hoping to get all that performance back. :-)

Bob
======================================
Bob Friesenhahn
[EMAIL PROTECTED], http://www.simplesystems.org/users/bfriesen/
GraphicsMagick Maintainer,    http://www.GraphicsMagick.org/