On 10/08/2010 07:15 PM, Gerald A wrote:
On Fri, Oct 8, 2010 at 4:55 PM, Andy Graybeal <[email protected] <mailto:[email protected]>> wrote:

    I'll have 2 firewalls, and 2 UPS's one for each firewall.

    Each firewall will have:
    1. a hot swap raid array (only two HD's set to RAID 1, mirroring).
    2. two hot swap power supplies.

    Is one UPS per firewall agreeable?  I don't know how to do it
    otherwise.  I can't imagine purchasing 4 UPS's, one for each power
    supply.  Seems a little overkill. I welcome any input.


Plug one hotswap supply from each firewall into both of the UPS boxes you have. That way, even if you have to service a UPS, you won't lose a firewall. I wouldn't dedicate a UPS to each firewall, because any UPS issue makes your bring down a box no matter what.


True, but depending on your configuration, another way to hook this up is to bypass the UPS for one of the power supplies on each firewall:

FW1 - Power supply 1 -> UPS1
FW1 - Power supply 2 -> straight to power grid

FW2 - Power supply 1 -> UPS2
FW2 - Power supply 2 -> straight to power grid

This way, you would still be up and running if both UPS systems fail for some reason. I've seen it happen! eg short circuit in a system connected to both UPS triggering both UPS to shutdown. (Try explaining complete power failure to your boss when all lights are still on in the entire building ;-) )

Agreed, during power grid failure, FW1 would go down if UPS1 fails, and FW2 would go down if UPS2 fails, but you got CARP to fix that.

Just my 2 cents.

Regards,

Hans