Adam 

I am shocked that the telco around you don't have redundant UPS 

Heck a large number of the cell towers we work with and around even have this 
Even N+1 cooling is in place 

But I agree - depending upon your needs what you lay out is / should be more 
than enough


On Oct 9, 2010, at 9:01 PM, Adam Thompson wrote:

> It’s perhaps overkill for many scenarios, but if you’re truly trying for 
> no-single-point-of-failure, buy UPSes from two different vendors, ideally 
> using two different technologies.  I’ve seen matched pairs of UPSes knocked 
> out by the same power event, and more commonly I’ve seen matched sets of 
> batteries fail without warning.  To clarify, there are power events that will 
> kill an APC SmartUPS whereas their BackUPS won’t even notice a problem; on 
> the other hand, the SmartUPS will protect a power supply against some failure 
> modes that a BackUPS cannot.  And a full-online-conversion UPS, while ideal, 
> costs an arm and a leg.  All three will tolerate different amounts of input 
> power phase mismatch (“Power Factor”).
>  
> It’s nearly impossible to design truly “uninterruptible” power; anyone who’s 
> installed a mainframe can attest to this!  You need capacitors on the circuit 
> board to smooth ripples (micro-events), ultracapacitors or batteries to prop 
> up the input power during sub-second (or even multi-second) outages, a 
> traditional UPS to provide interim power, a generator to cover long outages, 
> and a ground-zero-grade blast shelter to put it all in so it stays running in 
> case of global thermonuclear war… and even then, we still don’t have a 
> technology to work around the power outages anticipated when the heat death 
> of the universe occurs.
>  
> Yes, I’m being silly, but my point is that there’s no point in trying to 
> design a “perfect” system.  “Better than normal” is almost always what you’re 
> really reaching for.
> Having CARP failover is level 1, dual power supplies is level 2, dual UPSes 
> is level 3, how far do you plan to take this?  What if your ISP goes down – 
> are you also going to multi-home?  Are the devices behind this firewall also 
> multiply-redundant?
>  
> I don’t mean to suggest there’s no point in increasing reliability, but even 
> two UPSes is going far beyond the needs of most applications.  
> “Carrier-grade” doesn’t even mean having redundant UPSes… at least, none of 
> the telcos I work with in my region have redundant UPSes powering their phone 
> switches!
>  
> Anyway, like I said – if you’re going to run >1 UPS, use *different* UPSes to 
> avoid hitting the identical problem at the identical time on all of them, 
> which has actually happened to me.
>  
> -Adam
>  
>  
> From: Hans Maes [mailto:[email protected]] 
> Sent: Saturday, October 09, 2010 10:02
> To: [email protected]
> Subject: Re: [pfSense Support] Dual WAN + Firewall Redundancy + UPS 
> Redundancy (?) at entrance
>  
> 
> On 10/08/2010 07:15 PM, Gerald A wrote:
> 
> On Fri, Oct 8, 2010 at 4:55 PM, Andy Graybeal <[email protected]> 
> wrote:
> I'll have 2 firewalls, and 2 UPS's one for each firewall.
> 
> Each firewall will have:
> 1. a hot swap raid array (only two HD's set to RAID 1, mirroring).
> 2. two hot swap power supplies.
> 
> Is one UPS per firewall agreeable?  I don't know how to do it otherwise.  I 
> can't imagine purchasing 4 UPS's, one for each power supply.  Seems a little 
> overkill. I welcome any input.
> 
> Plug one hotswap supply from each firewall into both of the UPS boxes you 
> have. That way, even if you have to service a UPS, you won't lose a firewall. 
> I wouldn't dedicate a UPS to
> each firewall, because any UPS issue makes your bring down a box no matter 
> what.
> 
> 
> True, but depending on your configuration, another way to hook this up is to 
> bypass the UPS for one of the power supplies on each firewall:
> 
> FW1 - Power supply 1 -> UPS1
> FW1 - Power supply 2 -> straight to power grid
> 
> FW2 - Power supply 1 -> UPS2
> FW2 - Power supply 2 -> straight to power grid
> 
> This way, you would still be up and running if both UPS systems fail for some 
> reason. 
> I've seen it happen! eg short circuit in a system connected to both UPS 
> triggering both UPS to shutdown. 
> (Try explaining complete power failure to your boss when all lights are still 
> on in the entire building ;-) )
> 
> Agreed, during power grid failure, FW1 would go down if UPS1 fails, and FW2 
> would go down if UPS2 fails, but you got CARP to fix that.
> 
> Just my 2 cents.
> 
> Regards,
> 
> Hans
> 
> 

Reply via email to