> From: [email protected] [mailto:[email protected]]
> On Behalf Of Luke S. Crawford
> 
> My understanding is that my equipment runs more efficently on 208v
> than on 120v.

Not necessarily.  The problem is as simple as this:  Your equipment expects
steady DC voltage, and the power company provides AC.  When you go through
your A2D conversion, you have storage elements in your power supply which
continue to power the DC equipment while the AC voltage is on the downswing
or the backswing.  If the engineers aren't careful in the design of your DC
power supply, the stored energy may go to waste.  This is the difference
between VA and W.  VA is always >= W, and the difference between VA and W is
wasted in heat.  Ideally, you want your power factor (pf) to be precisely
1.0.  This means VA=W, and perfect efficiency in the A2D conversion.
Perfection is not realistic, but something over 95% efficiency is very
realistic.

So there are a few ways of dealing with this.  You can use 2-phase or
3-phase power (240V or 208V) to create a smoother AC power signal, thus
utilizing less storage elements, and producing less waste.  That is true.
Or you can just design a smarter A2D power supply, which efficiently uses
the 120V single phase power.

Since 208V 3-phase power is rare, it's expensive.  Most (but not all)
equipment manufacturers have decided to address the problem by selling
smarter power supplies.  For example, I have a small farm of generic black
boxes, and when I measure the VA and W of these systems, I see something
like 60% efficiency.  Loads of waste.  But when I hook up my kill-a-watt to
a Dell server or workstation...  Just the "typical" ones, without the Dell
Upgraded "Green" or "Eco friendly" power supplies...  I get no less than 95%
efficiency.  I can only imagine the "green" power supplies must be something
like 99% efficient.

So.  In the end, Luke:  Your curiosity about 120V single-phase, versus 240V
or 208V, 2 or 3 phase...  Depends on your equipment.  If you can, you should
measure the VA and W consumption of your equipment, and let that be your
guide, Re: whether or not you care about more phased power.