> From: [email protected] [mailto:[email protected]]
> On Behalf Of Tracy Reed
> 
> they currently have to run me 4 20A per rack. Coudldn't they cut
> that
> approximately in half (power factor correction etc, as mentioned earlier)
if I
> ran 208v? 

Depends what you call "cut it in half."
If you have a single 20A 120V circuit, as compared to a single 20A 3-phase
208V circuit...  Well, indeed you have three 120V lines bundled into the
3-phase circuit, so it's three times as many hot wires, but it's less than
twice the effective voltage, but it's able to draw a smoother current, less
spiky, which means you're less prone to blowing circuit breakers.  

All in all, I would say, yes you're approximately able to power twice as
much equipment (a little more, say ~2.3x) with a 208V 3-phase power supply
as compared with the 120V single-phase.  And since they're billing you by
the Volt-Amp-Hour, remember one thing:  Supposing you have non-stupid power
supplies in your equipment, you were already getting a power factor of
around 0.95 in your 120V equipment.  You might get a little better, say 0.99
with your 3-phase power supply, but the difference is marginal.  Which
means, for all intents and purposes, 1VAh ~= 1VAh.  By changing the way you
deliver your power, you have not changed how much power you consume.  (Just
marginally.)

If you're trying to reduce energy costs, the only number you need to look at
is the cost per VAh, and whatever few percent marginal PF gain you might get
by changing how you deliver your power.