On Wed, Feb 29, 2012 at 9:15 AM, Luke S. Crawford <[email protected]> wrote:

> The three-phase 208v that coresite santa clara wants to charge me more
> for? I believe that is three 120v hots, and therefore, rather more power
> than what I'm probably incorrectly refering to as 'single phase' 208v,
> and something I could not plug directly into my servers without buying
> new PSUs.
>

The 208v circuits I've used are 3-phase and you can use them with normal
PSUs (like the stock ones in your Supermicro servers). The PDU takes
3-phase 208v input and outputs 208v that the servers can use (single
phase?). I think that's the case for all 3-phase PDUs with C13 outputs, at
least it is for ServerTech units I've used.

You would use a PDU like this:
http://www.servertech.com/products/switched-pdus/switched-pdu-cw-24vd-vy-3ph

-Anton