Wow, I had not gotten that far with bench testing to observe that. My tower is 
grounded properly so I would have found out the hard way when +48 power managed 
to find its way back into the equipment cabinet through the tower grounding 
system! I can understand now why you need the isolated DC converter. With one 
rated at 200 watts, I think you need 1 RSD-200C for each BreezeCompact?

Matt Lauer
Solvaris, Inc.

586.453.0440 p
248.495.3977 c
586.453.0805 f

[email protected] <mailto:[email protected]>
www.solvaris.com <http://www.solvaris.com/>
> On Dec 21, 2016, at 2:01 PM, Adam Moffett <[email protected]> wrote:
> 
> Matt,
>  
> We're actually running without the power supply grounded at most sites, but 
> it doesn't matter for the equipment smoking issue because the Compact has DC+ 
> connected to it's chassis ground.  You can verify this by measuring for 
> voltage or resistance between the negative terminal on your power supply and 
> the ground lug or mounting bracked on your Compact.  If you have a +48 device 
> on the tower which also has a chassis ground connected to DC then it won't 
> matter whether or not you have a ground at the bottom.....you'll have a short 
> through the tower and either blow a fuse or smoke something.
>  
> What should be safe in that mixed DC environment, in my opinion, is an 
> isolated 48v to 48v converter such as a Meanwell RSD-200C-48 or equivalent.  
> You put it between your rectifier and the Compact power cable.
>  
> Good luck out there,
> Adam
>  
>  
> ------ Original Message ------
> From: "Matt Lauer" <[email protected] <mailto:[email protected]>>
> To: [email protected] <mailto:[email protected]>
> Sent: 12/21/2016 8:54:09 AM
> Subject: [Telrad] Neg 48 on BreezeCompact 1000
>  
>> I have a BreezeCompact 1000 powered up on the bench. I read the installation 
>> manual and I do see it is advised to connect “+ Output to Site Ground” per 
>> page 24 of the manual. I have mixed equipment in our tower cabinet so we 
>> have a floating ground - neither a negative or a positive is bonded to the 
>> cabinet/chassis ground.  I will burn up other equipment if I positively 
>> ground the + output from our rectifier. Is anyone else running Telrad in 
>> production with a floating ground? 
>> 
>> Matt Lauer
>> Solvaris, Inc.
>> 
>> 586.453.0440 p
>> 248.495.3977 c
>> 586.453.0805 f
>> 
>> [email protected] <mailto:[email protected]>
>> www.solvaris.com <http://www.solvaris.com/>