On 14 August 2014 13:47, Richard Savage <[email protected]> wrote:

>  Hi
>
>
>
> I am testing some new Cisco ASR901’s and need to find a suitable DC power
> supply that will power them up in a lab environment.  The ASR 901-12C-F-D
> says that it will accept:
>
>
>
> 1 GE models:
>
> ● DC-input voltage rating: 24 VDC, -48 VDC, -60 VDC
>
> ● DC-input current rating: 2.5A maximum for non- TDM variants and 3.0A
> maximum for TDM variants
>
>
>
> Power connector
>
> 6-position 2-tier stacked connector comprising two feeds, A and B DC power
> (AMPHENOL ELVA06100), and 3‑position mating connectors for each feed
> (AMPHENOL ELVP03100)
>
>
>
> Does anyone have any suggestions to a Lab DC power supply?
>
>
Buy a proper one ? :)

The following won't be easy, but may be free if you have the right stuff
lying around. It depends how much a "real" PSU is for this purpose and how
much experience you have in-house with electronics.

If you have a pile of them lying around, you could use some types of ATX
PSUs (they'll need modified) as long as the outputs *and* their cases are
fully isolated from each other (this needs properly checking- if the cases
are at earth potential then you've just created a bigger problem) You'd
chaining the outputs together in series to get +24V (2x12V) -48V (4x12V)
-60V (5x12V). You'll have plenty of amps, so much that you'll definitely
need to fit appropriate fuses to prevent fires and popping the mains
circuit breaker should a fault occur. Personally I'd use 2A to 3A fuses
(max) and 10A cables as a start, going to lower fuses is possible. the
fuses will protect the wiring, any fuses internal to the router protect
only the router equipment internally, so you'd need to use 30A+ cable to it
otherwise ;)

In the worst-case, you'd need a maximum of 11 ATX PSUs, best-case you'd get
away with 7.  They'll need carefully selected for their isolation designs,
modified with suitable minumum-loads added and appropriate fuses or
breakers for the low current you require. Get an experienced electrical or
electronics engineer to modify them and connect them up, our you'll have
800*11=8 kiloWatts of DC fire on your hands, pulling 15% more than that
from the mains circuit - not good.
The max power draw with the router as load will be far less, minus the
efficiency of each one and the static load resistors you've added (10-20W
per PSU for those resistors - don't omit them!) You're talking about a quid
or two for the resistors for each PSU at most, so £20 should see them
modified for continuous use. Omitting these resistors could cause the PSU
output (especially the -60V one) to rise to a damaging level because the
offload rise will be 5x that of one unloaded PSU. You;ll quickly have a
popped router on your hands otherwise.

This means that this route is a horrible bodge, but I've used series chains
of ATX PSUs for over several hundreds Volts of DC before in a lab
environment, because with the right ones and the right modifications are
very versatile - you can reconfigure them to any sum of 12V, 5V and 3.3 at
high currents and both negative and positive outputs. Using discarded PSUs
they are effectively free other than the offload resistors and wiring the
PS_ONs together.

This is *not* a job for an amateur, it needs a lot of safety thought and
bench sense. The risk assessment will be several pages alone and needs done
right in case someone gets killed. Done right it's as safe series connected
lab-PSU setup. You also need to understand that above 60V potential (in
this case, wired at minus 60 volts WRT Terra) is above the old SELV limit,
so the wiring should be done by a competent professional and appropriately
insulated.

In particular, you need to select the cabling to match the over-curent
protection, though you'll need to do that with a -48V "rectifier pack" too
(they tend to boatload of amps out for whole racks), so safety requires fat
wiring or fitting additional overcurrent protection. When they go wrong
they are a free-running arc welder and electric heater rolled into one -
imagine 30+Amps on thin cables that can handle 6A plugged into the router.
If there's no fuse, the entire length wire is the fuse, so it catches fire.
The foldback or crowbar probably won't sense a short at 3/4/5/6A and so
keep on pumping amps down the wires thinking that it's got a rackfull of
items and batteries to supply.

To buy new PSUs, you can get generic 24V and 48V PSU from various sources,
the 60v is less common as a cased PSU, all will need suitably enclosed and
isolated from each other. You'd be looking at 30-100 quid for each as
separates for low-reliability ones and they may need better output
smoothing. You could buy cheaper on Ebay, 24V is a very common PSU output
and there are many sources available. It's up to you to trust the cheaper
ones - I'd rather use my own ATX series-PSUs.


On a side note - older low-end Cisco router and switch redundant power
supply inputs could be freaked by cutting up an  ATX PSU <> motherboard
 Molex Mini-Fit Junior connector and feeding them from a single modified
ATX PSU. the 5v and 12V rails were easy. Great dodge for when the internal
PSU pops and you have no RPS.
You may find that single pins cut from a Mini-Fit Jr fit the back of your
new router too? May save you crimping your own if you are careful with a
Stanley knife and have big heatsink to cover it all with a couple of good
layers.


--