That is why there are nice things like, "Test fails when exceeded" and
"Logging Triggers".

:)

Tv


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Glatt, Robert
Sent: Wednesday, March 12, 2003 2:16 PM
To: '[EMAIL PROTECTED]'
Subject: RE: [WhatsUp Forum] Monitoring options for APC UPS


IMHO...if you create a service that monitors a MIB value then you run the
risk of a false condition. If you wait to receive the trap you will always
be right as long as the trap was received. I use the first condition and if
the network is slow then the WUG server does not get a response to the mib
query. therefore the answer does not equal my "up" value and returns a down
condition. Not really a true down. I guess which one you use depends on the
quality of your network and how right you have to be.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]
Sent: Wednesday, March 12, 2003 3:05 PM
To: [EMAIL PROTECTED]
Subject: RE: [WhatsUp Forum] Monitoring options for APC UPS



Hi, people.

This may be a stupid question, but I'd be even stupider if I didn't ask it,
and continued not to know.......

What is the difference between allowing an SNMP trap (UPS on Battery/power
restored) to notify of the battery condition and creating the SNMP
monitoring entry below (upsbasicOutputStatus)??

Chris Powers
Systems Engineer
MCSE, CNA, Network+, A+
Keane IT Technical Services
(617) 517-1730




                    "Glatt, Robert"

                    <[EMAIL PROTECTED]>                To:
"'[EMAIL PROTECTED]'"
                    Sent by:
<[EMAIL PROTECTED]>
                    [EMAIL PROTECTED]       cc:

                    switch.com                        Subject:     RE:
[WhatsUp Forum] Monitoring options for APC UPS




                    03/12/2003 02:46 PM

                    Please respond to

                    WhatsUp_Forum









1.3.6.1.4.1.318.1.1.1.4.1.1.0  upsBasicOutputStatus

online = 2
onbattery = 3

you may also want to check the hardware version on the ups itself. An older
version my not support all the mib values.
     -----Original Message-----
     From: [EMAIL PROTECTED]
     [mailto:[EMAIL PROTECTED]
     Sent: Wednesday, March 12, 2003 2:32 PM
     To: [EMAIL PROTECTED]
     Subject: RE: [WhatsUp Forum] Monitoring options for APC UPS


     well I dug into the MIBs to get some good oid's to monitor.  I can't
     find one that explicitly tells me that it's on line or battery power,
     but I did find a "TimeOnBattery" oid, and when polled it returns a 0,
     probably indicating that it's NOT on battery.

     But when I create an SNMP service monitor in WUG to monitor this MIB
     it fails/doesn't work.... (I have another monitor I created for the
     "ReplaceBattery" OID and that seems to work fine), so now I ned help
     in understanding the debug log of my SNMPMON

     it says:

     Check Complete (-1) ups1 : 01: APCTimeOnBattery


     I'm assuming the -1 means that it failed, but how can I narrow down
     what failed, did it get a value back?  is the 01 the value it
     returned?  When I browse it via a separate mib browser it always
     returns a 0.  The value of this oid is listed as TimeTicks, could that
     be screing something up in WUG?

     Thanks for any help,





     Please respond to [EMAIL PROTECTED]


     Sent by:        [EMAIL PROTECTED]


     To:        [EMAIL PROTECTED]
     cc:
     Subject:        RE: [WhatsUp Forum] Monitoring options for APC UPS

     One of the variables you will be interested in is the results of the
     self-test.  The box will do a self test every two weeks (default, can
     be set to one week or off).  If the self-test fails,
     you'll want to be taking action soon, preferably before the next self
     test or a power outage.

     Jay.

     At 10:49 AM 3/12/2003 -0600, you wrote:
     there are a few different mibs that can be looked at depending on what
     you really want to know.

     There is upsBasicBatteryStatus - with 3 variables, unknown, normal or
     low
                upsBasicOutputStatus -which tells you the current state of
     the UPS

     I would suggest printing out the powernet.mib and picking the one(s)
     that fit your  needs
     -----Original Message-----
     From: [EMAIL PROTECTED] [
     mailto:[EMAIL PROTECTED]
     Sent: Wednesday, March 12, 2003 11:38 AM
     To: [EMAIL PROTECTED]
     Cc: [EMAIL PROTECTED]
     Subject: Re: [WhatsUp Forum] Monitoring options for APC UPS

     >>BatteryStatus 1.3.6.1.4.1.318.1.1.1.2.1.1.0 (UP if =2)



     Not wanting to dig into the MIB, what exactly does this mean?

     does it mean if the value is = 2 then the UPS in on 'line' power, and
     any other value means that the UPS is on 'Battery' Power?

     As you can tell, I want a way to monitor whether the powere supplying
     the UPS is ON or OFF.







     Please respond to [EMAIL PROTECTED]

     Sent by:        [EMAIL PROTECTED]

     To:        [EMAIL PROTECTED]
     cc:
     Subject:        Re: [WhatsUp Forum] Monitoring options for APC UPS

     Hi!

     First of all you must have a network card for you APC UPS ;)
     Then you can monitor ICMP (is the UPS still alive) and a lot of SNMP
     values.

     We monitor:
     BatteryNeededReplacement 1.3.6.1.4.1.318.1.1.1.2.2.4.0 (UP if =1)
     BatteryStatus 1.3.6.1.4.1.318.1.1.1.2.1.1.0 (UP if =2)
     InputVoltage 1.3.6.1.4.1.318.1.1.1.3.2.1.0 (between 210 and 250 volts
     is
     ok)

     There are additional values to monitor, for ex. internal temperature,
     look
     in APC MIB base
     (SNMP MIB base is included into your APC CD or is available from www.)

     -------------------------------
     Edgars Smilgzdruvs
     IT division, LMT
     PH: +371-9248674





     |---------+------------------------------------->
     |         |           "Garth Fish"              |
     |         |           <[EMAIL PROTECTED]|
     |         |           .com>                     |
     |         |           Sent by:                  |
     |         |           [EMAIL PROTECTED]|
     |         |           pswitch.com               |
     |         |                                     |
     |         |                                     |
     |         |           12.03.2003 00:27          |
     |         |           Please respond to         |
     |         |           WhatsUp_Forum             |
     |         |                                     |
     |---------+------------------------------------->
      >

----------------------------------------------------------------------------
--------------------------------------------------|


      |
     |
      |       To:       <[EMAIL PROTECTED]>
     |
      |       cc:       "Garth Fish" <[EMAIL PROTECTED]>
     |
      |       Subject:  [WhatsUp Forum] Monitoring options for APC UPS
     |
      >

----------------------------------------------------------------------------
--------------------------------------------------|






     Greetings and salutations!



     I am new to the realm of What's Up Gold monitoring.  We are just in
     the
     early stages of development for the monitoring of all our servers and
     ups'.
     My question is, what monitoring options via WUG are available to me
     for an
     APC smart UPS? Thank you in advance.



          Garth Fish
          Support Analyst
          OSI Support Services, Inc.
          2520 South 170th Street
          New Berlin, WI 53151
          T: (262) 780-2000 x3314 or (800) 984-3431
          F: (262) 780-2080



            E: mailto:[EMAIL PROTECTED]





     Outsourcing services are primarily performed by OSI Outsourcing
     Services,
     Inc.; collection services are primarily performed by OSI Collection
     Services, Inc.; letter series collection services are primarily
     performed
     by North Shore Agency, Inc. and Transworld Systems, Inc.; portfolio
     services are performed by OSI Portfolio Services, Inc.

     This message (including any attachments) contains confidential
     information
     intended for a specific individual and purpose, and is protected by
     law.
     If you are not the intended recipient, you should delete this message
     and
     are hereby notified that any disclosure, copying, or distribution of
     this
     message, or the taking of any action based on it, is strictly
     prohibited.

















     Please visit http://www.ipswitch.com/support/mailing-lists.html
     to be removed from this list.

     An Archive of this list is available at:
     http://www.mail-archive.com/whatsup_forum%40list.ipswitch.com/





Please visit http://www.ipswitch.com/support/mailing-lists.html
to be removed from this list.

An Archive of this list is available at:
http://www.mail-archive.com/whatsup_forum%40list.ipswitch.com/

Please visit http://www.ipswitch.com/support/mailing-lists.html
to be removed from this list.

An Archive of this list is available at:
http://www.mail-archive.com/whatsup_forum%40list.ipswitch.com/


Please visit http://www.ipswitch.com/support/mailing-lists.html 
to be removed from this list.

An Archive of this list is available at:
http://www.mail-archive.com/whatsup_forum%40list.ipswitch.com/

Reply via email to