--- On Tue, 9/16/08, Albert <[EMAIL PROTECTED]> wrote:

> From: Albert <[EMAIL PROTECTED]>
> Subject: [Repeater-Builder] Volt-Amp    (Re: APC UPS Charging Power)
> To: Repeater-Builder@yahoogroups.com
> Date: Tuesday, September 16, 2008, 5:12 PM
> Hopefully you will forgive me hijacking the post but this
> brings up a 
> question I have had for a long time. What on earth is a
> "volt-amp". 
> My logic would state that is is the same as a watt, which
> is volts x 
> amps, as you probably well know. So what on earth is is?
> 
> Confused.....
> 
> Albert
> 
> 
If you only have a resistance element then the watt and volt-amp are the same.  
It should really be VAR or volt-amp reactive.  If the load has a very high 
reactance (capacitive or inductive) , the volt and amp will be  out of phase.  
That is the maximum point on a voltage curve will not be at the same time as 
the maximum amp point.  When you turn on a switch from a battery going through 
a resistor and put a voltmeter across the capacitor and an amp meter in series, 
the voltmeter will slowly start to rise and the amp meter will read maximum and 
then fall.  This is a crude example as how the current and voltage get out of 
phase.



      