Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-17 Thread Chuck Kelsey
Spinning disk meters are becoming a thing of the past. However, I believe 
that very few utilities are billing residential customers for kVAR. Many do 
charge residential demand and time-of-day rates. Eric, you may want to 
comment further.

Chuck
WB2EDV



- Original Message - 
 As I stated in an earlier post, the rotating-disk kWH meter on the typical
 residence measures only true power.  It does this magic by combining the
 magnetic fields of two coils: a voltage coil that is connected in parallel
 with the load, and a current coil that is in series with the load.  The
 angular displacement of these coil windings is precisely set so that only
 currents that are exactly in phase with the voltage result in a torque to
 turn the aluminum disk. 



RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-17 Thread Jim Brown
I have a site where for many years the only load was a battery charger feeding 
a battery to power up the equipment.  For many years the power meter DID NOT 
MOVE!  It started moving when I substituted a GE Mastr II base station power 
supply with backup battery.

My theory (correct me if I am wrong) is that the very short duty cycle current 
pulses drawn when the sine wave is at the crest of the cycle (when the diodes 
conduct) is why the meter was not moving.

The GE Power supply is ferro resonant and draws current over the whole cycle 
although the power factor is pretty bad.  The GE supply also uses a filter 
choke which reduces the current pulsing when the diodes conduct to a minimum.

73 - Jim  W5ZIT

--- On Tue, 9/16/08, Bob M. [EMAIL PROTECTED] wrote:
From: Bob M. [EMAIL PROTECTED]
Subject: RE: [Repeater-Builder] Volt-Amp(Re: APC UPS Charging Power)
To: Repeater-Builder@yahoogroups.com
Date: Tuesday, September 16, 2008, 10:31 PM











Thank you Eric. This was the explanation I was looking for. The UPS 
is saving me money when drawing 181 Volt-Amps, yet the electric meter is only 
recording and charging me for 31 Watts. I wonder if APC did this on purpose. I 
don't know how much current is actually being fed to the batteries; they've 
been in there for a couple of months and should be fully charged by now, so it 
should just be trickling them (eight 12V 7A SLA cells in series/parallel for 
48V).



Bob M.

==

--- On Tue, 9/16/08, Eric Lemmon [EMAIL PROTECTED] net wrote:



 From: Eric Lemmon [EMAIL PROTECTED] net

 Subject: RE: [Repeater-Builder] Volt-Amp(Re: APC UPS Charging Power)

 To: Repeater-Builder@ yahoogroups. com

 Date: Tuesday, September 16, 2008, 9:21 PM

 Albert,

 

 You are forgiven, because you pose an important question!

 

 The spinning aluminum disk in the kilowatthour meter found

 on most

 residential service-entrance panels measures true power in

 kilowatts versus

 time, which equals energy.  Thus, your electric utility

 charges you for the

 true power you use, not for volts times amperes- known as

 reactive power.

 Although the utility must provide the capability to supply

 all of the

 amperes you need, some of those amperes are given

 back to the utility due

 to a lower than unity power factor.  That is why many

 utility companies

 charge a kVAR Penalty to certain industrial

 power users whose volt-ampere

 demands far exceed their watt demands, meaning that the

 power factor is low.

 Industrial power users strive to keep their power factors

 at 0.95 or above,

 to avoid some really painful penalties!  The power factor,

 or PF, is simply

 watts divided by volts time amperes.

 

 The issue of power factor is why large Diesel generator

 sets have ratings

 such as 1000 kW/1250 kVAR.  In simple terms, any AC

 generator requires

 torque (engine horsepower) to meet true power demands, and

 excitation (field

 flux intensity) to meet reactive power demands.  When the

 generator load is

 reactive, that is, it has a power factor less than unity,

 the generator must

 not only have the horsepower to supply the energy in watts,

 but it must have

 excess capacity to handle the additional current required

 by motors and

 other low-power-factor loads.  In a nutshell, that is why a

 1000 watt

 generator may be unable to keep running a refrigerator that

 uses only 900

 watts; the fridge may require 1200 VA to operate because it

 has a low power

 factor, and the small generator has no ability to handle

 such loads.

 Because of its relatively small amount of spinning mass,

 such a small

 generator probably could not even handle the

 refrigerator' s starting

 current- which is about 5 to 6 times its running current.

 

 73, Eric Lemmon WB6FLY

 

 ___

 

















  

Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-17 Thread Chuck Kelsey
More likely the meter simply failed to register well on light loads. It 
doesn't happen with the newer meters.

Chuck
WB2EDV



- Original Message - 
From: Jim Brown
To: Repeater-Builder@yahoogroups.com
Sent: Wednesday, September 17, 2008 10:06 AM
Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)


I have a site where for many years the only load was a battery charger 
feeding a battery to power up the equipment.  For many years the power meter 
DID NOT MOVE!  It started moving when I substituted a GE Mastr II base 
station power supply with backup battery.

My theory (correct me if I am wrong) is that the very short duty cycle 
current pulses drawn when the sine wave is at the crest of the cycle (when 
the diodes conduct) is why the meter was not moving.

The GE Power supply is ferro resonant and draws current over the whole cycle 
although the power factor is pretty bad.  The GE supply also uses a filter 
choke which reduces the current pulsing when the diodes conduct to a 
minimum.

73 - Jim  W5ZIT




Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-17 Thread WD7F - John in Tucson
Thank you Eric Lemmon !  Your explanation is the most precise I've read thus 
far.
The last line of your last paragraph said what folks want to hear.  I 
started to respond
to this thread earlier, but after a few minutes of organizing my thoughts, 
my aging pea-brain
said, Forget this and go get another gin  tonic !  What's another few 
brain cells anyway ?

de WD7F
John in Tucson

- Original Message - 
From: Eric Lemmon [EMAIL PROTECTED]
To: Repeater-Builder@yahoogroups.com
Sent: Tuesday, September 16, 2008 9:59 PM
Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)


 John,

 You are correct that when the power factor is 1.00, the current is in 
 phase
 with the voltage, as it will be in a purely resistive circuit.  In this
 unique case, watts equals volt-amperes.  However, when the load is 
 reactive,
 the current either leads or lags the applied voltage.  A typical case is a
 lightly-loaded induction motor, which may exhibit a power factor around
 0.65, which is considered to be a poor PF.  Some of the current drawn by
 this motor is used to create torque and perform actual work, and this
 current is nearly in phase with the applied voltage.  Some current causes
 heating of the copper windings and the field core, and this current is 
 also
 nearly in phase with the applied voltage.  Both of these currents consume
 true power and are measured in watts.  However, a significant amount of
 current does nothing but magnetize the field windings during part of the 
 AC
 cycle, and that reactive energy is returned to the source as the magnetic
 field collapses just before the field is built up with the opposite 
 polarity
 during the other half of the AC cycle.  There are additional reactive
 losses, such as eddy-current and hysteresis losses, but the magnetizing
 currents are lagging the applied voltage, so they are the cause of 
 apparent
 power which is expressed in volt-amperes reactive, also known as VARs.

 As was discussed at great length in this forum several months ago, one
 cannot measure true power with separate voltage and current meters.  That 
 is
 because the readings of separate meters are not synchronized in time. 
 Even
 if one uses two true RMS DVMs to measure voltage and current, one still
 winds up with nothing more than apparent power based upon volts times
 amperes, or volt-amperes.

 To measure true power, one must use an AC power meter that synchronously
 measures current and voltage throughout the entire cycle.  This can be
 performed by a device called a four-quadrant multiplier which, as its 
 name
 implies, performs the multiplication of current and voltage through 360
 degrees of phase rotation.  One such instrument is a VIZ Instruments 
 WD-767
 Digital Wattmeter, which sold for about $925.  Another device which has
 become very popular with Hams is the Kill-A-Watt meter that costs about
 $20 from several Internet vendors.  Although not as accurate as the 
 WD-767,
 it does perform quite well.

 As I stated in an earlier post, the rotating-disk kWH meter on the typical
 residence measures only true power.  It does this magic by combining the
 magnetic fields of two coils: a voltage coil that is connected in parallel
 with the load, and a current coil that is in series with the load.  The
 angular displacement of these coil windings is precisely set so that only
 currents that are exactly in phase with the voltage result in a torque to
 turn the aluminum disk.  A small permanent magnet is placed near the disk 
 so
 that the speed of the disk is proportional to the amount of true power 
 being
 consumed.  Since speed is movement over time, the disk is geared to a
 register that accumulates the number of rotations, which represents power
 over time, which is energy.  Thus, the meter measures kilowatthours.  You
 pay only for the true power that you actually use; you do not pay for
 apparent power since volt-amperes is not true power.

 73, Eric Lemmon WB6FLY


 -Original Message-
 From: Repeater-Builder@yahoogroups.com
 [mailto:[EMAIL PROTECTED] On Behalf Of John Barrett
 Sent: Tuesday, September 16, 2008 9:13 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

 This doesn't mesh up with what I've learned about power factor -- the
 impression that I got was a perfect power factor was 1 (one) (current in
 phase with voltage, equipment using everything the the power company
 charges you for to do useful work). Anything other than PF=1 meant that
 the equipment was using the power less efficiently, and therefore you
 were paying more in KWH than the work actually performed. That
 description excludes the possibly that the equipment could use more
 power than the power company records as being delivered (heck,
 conservation of energy says that in any case). any load reactance
 (inductive or capacitive) and the very low PF numbers stated sound more
 like what I get off my linear power supplies

Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-17 Thread Doug Zastrow
Eric,

Kudos on a great explanation

Doug
  - Original Message - 
  From: Eric Lemmon 
  To: Repeater-Builder@yahoogroups.com 
  Sent: Tuesday, September 16, 2008 11:59 PM
  Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)


  John,

  You are correct that when the power factor is 1.00, the current is in phase
  with the voltage, as it will be in a purely resistive circuit.  In this
  unique case, watts equals volt-amperes.  However, when the load is reactive,
  the current either leads or lags the applied voltage.  A typical case is a
  lightly-loaded induction motor, which may exhibit a power factor around
  0.65, which is considered to be a poor PF.  Some of the current drawn by
  this motor is used to create torque and perform actual work, and this
  current is nearly in phase with the applied voltage.  Some current causes
  heating of the copper windings and the field core, and this current is also
  nearly in phase with the applied voltage.  Both of these currents consume
  true power and are measured in watts.  However, a significant amount of
  current does nothing but magnetize the field windings during part of the AC
  cycle, and that reactive energy is returned to the source as the magnetic
  field collapses just before the field is built up with the opposite polarity
  during the other half of the AC cycle.  There are additional reactive
  losses, such as eddy-current and hysteresis losses, but the magnetizing
  currents are lagging the applied voltage, so they are the cause of apparent
  power which is expressed in volt-amperes reactive, also known as VARs.

  As was discussed at great length in this forum several months ago, one
  cannot measure true power with separate voltage and current meters.  That is
  because the readings of separate meters are not synchronized in time.  Even
  if one uses two true RMS DVMs to measure voltage and current, one still
  winds up with nothing more than apparent power based upon volts times
  amperes, or volt-amperes.

  To measure true power, one must use an AC power meter that synchronously
  measures current and voltage throughout the entire cycle.  This can be
  performed by a device called a four-quadrant multiplier which, as its name
  implies, performs the multiplication of current and voltage through 360
  degrees of phase rotation.  One such instrument is a VIZ Instruments WD-767
  Digital Wattmeter, which sold for about $925.  Another device which has
  become very popular with Hams is the Kill-A-Watt meter that costs about
  $20 from several Internet vendors.  Although not as accurate as the WD-767,
  it does perform quite well.

  As I stated in an earlier post, the rotating-disk kWH meter on the typical
  residence measures only true power.  It does this magic by combining the
  magnetic fields of two coils: a voltage coil that is connected in parallel
  with the load, and a current coil that is in series with the load.  The
  angular displacement of these coil windings is precisely set so that only
  currents that are exactly in phase with the voltage result in a torque to
  turn the aluminum disk.  A small permanent magnet is placed near the disk so
  that the speed of the disk is proportional to the amount of true power being
  consumed.  Since speed is movement over time, the disk is geared to a
  register that accumulates the number of rotations, which represents power
  over time, which is energy.  Thus, the meter measures kilowatthours.  You
  pay only for the true power that you actually use; you do not pay for
  apparent power since volt-amperes is not true power.

  73, Eric Lemmon WB6FLY
   

  -Original Message-
  From: Repeater-Builder@yahoogroups.com
  [mailto:[EMAIL PROTECTED] On Behalf Of John Barrett
  Sent: Tuesday, September 16, 2008 9:13 PM
  To: Repeater-Builder@yahoogroups.com
  Subject: Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

  This doesn't mesh up with what I've learned about power factor -- the 
  impression that I got was a perfect power factor was 1 (one) (current in 
  phase with voltage, equipment using everything the the power company 
  charges you for to do useful work). Anything other than PF=1 meant that 
  the equipment was using the power less efficiently, and therefore you 
  were paying more in KWH than the work actually performed. That 
  description excludes the possibly that the equipment could use more 
  power than the power company records as being delivered (heck, 
  conservation of energy says that in any case). any load reactance 
  (inductive or capacitive) and the very low PF numbers stated sound more 
  like what I get off my linear power supplies with big capacitance and no 
  power factor correction. In any case, anything other than PF=1 should 
  mean that you are paying for more power than you are actually using.

  Tell me where I goofed this up ??

  Bob M. wrote:
  
   Thank you Eric. This was the explanation I was looking

Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread Ralph Mowery



--- On Tue, 9/16/08, Albert [EMAIL PROTECTED] wrote:

 From: Albert [EMAIL PROTECTED]
 Subject: [Repeater-Builder] Volt-Amp(Re: APC UPS Charging Power)
 To: Repeater-Builder@yahoogroups.com
 Date: Tuesday, September 16, 2008, 5:12 PM
 Hopefully you will forgive me hijacking the post but this
 brings up a 
 question I have had for a long time. What on earth is a
 volt-amp. 
 My logic would state that is is the same as a watt, which
 is volts x 
 amps, as you probably well know. So what on earth is is?
 
 Confused.
 
 Albert
 
 
If you only have a resistance element then the watt and volt-amp are the same.  
It should really be VAR or volt-amp reactive.  If the load has a very high 
reactance (capacitive or inductive) , the volt and amp will be  out of phase.  
That is the maximum point on a voltage curve will not be at the same time as 
the maximum amp point.  When you turn on a switch from a battery going through 
a resistor and put a voltmeter across the capacitor and an amp meter in series, 
the voltmeter will slowly start to rise and the amp meter will read maximum and 
then fall.  This is a crude example as how the current and voltage get out of 
phase.



  


RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread Eric Lemmon
Albert,

You are forgiven, because you pose an important question!

The spinning aluminum disk in the kilowatthour meter found on most
residential service-entrance panels measures true power in kilowatts versus
time, which equals energy.  Thus, your electric utility charges you for the
true power you use, not for volts times amperes- known as reactive power.
Although the utility must provide the capability to supply all of the
amperes you need, some of those amperes are given back to the utility due
to a lower than unity power factor.  That is why many utility companies
charge a kVAR Penalty to certain industrial power users whose volt-ampere
demands far exceed their watt demands, meaning that the power factor is low.
Industrial power users strive to keep their power factors at 0.95 or above,
to avoid some really painful penalties!  The power factor, or PF, is simply
watts divided by volts time amperes.

The issue of power factor is why large Diesel generator sets have ratings
such as 1000 kW/1250 kVAR.  In simple terms, any AC generator requires
torque (engine horsepower) to meet true power demands, and excitation (field
flux intensity) to meet reactive power demands.  When the generator load is
reactive, that is, it has a power factor less than unity, the generator must
not only have the horsepower to supply the energy in watts, but it must have
excess capacity to handle the additional current required by motors and
other low-power-factor loads.  In a nutshell, that is why a 1000 watt
generator may be unable to keep running a refrigerator that uses only 900
watts; the fridge may require 1200 VA to operate because it has a low power
factor, and the small generator has no ability to handle such loads.
Because of its relatively small amount of spinning mass, such a small
generator probably could not even handle the refrigerator's starting
current- which is about 5 to 6 times its running current.

73, Eric Lemmon WB6FLY

 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Albert
Sent: Tuesday, September 16, 2008 2:13 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

Hopefully, you will forgive me for hijacking the post, but this brings up a
question I have had for a long time. What on earth is a volt-amp?
My logic would state that is is the same as a watt, which is volts x amps,
as you probably well know. So what on earth is it?

Confused.

Albert



RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread Bob M.
Thank you Eric. This was the explanation I was looking for. The UPS is saving 
me money when drawing 181 Volt-Amps, yet the electric meter is only recording 
and charging me for 31 Watts. I wonder if APC did this on purpose. I don't know 
how much current is actually being fed to the batteries; they've been in there 
for a couple of months and should be fully charged by now, so it should just be 
trickling them (eight 12V 7A SLA cells in series/parallel for 48V).

Bob M.
==
--- On Tue, 9/16/08, Eric Lemmon [EMAIL PROTECTED] wrote:

 From: Eric Lemmon [EMAIL PROTECTED]
 Subject: RE: [Repeater-Builder] Volt-Amp(Re: APC UPS Charging Power)
 To: Repeater-Builder@yahoogroups.com
 Date: Tuesday, September 16, 2008, 9:21 PM
 Albert,
 
 You are forgiven, because you pose an important question!
 
 The spinning aluminum disk in the kilowatthour meter found
 on most
 residential service-entrance panels measures true power in
 kilowatts versus
 time, which equals energy.  Thus, your electric utility
 charges you for the
 true power you use, not for volts times amperes- known as
 reactive power.
 Although the utility must provide the capability to supply
 all of the
 amperes you need, some of those amperes are given
 back to the utility due
 to a lower than unity power factor.  That is why many
 utility companies
 charge a kVAR Penalty to certain industrial
 power users whose volt-ampere
 demands far exceed their watt demands, meaning that the
 power factor is low.
 Industrial power users strive to keep their power factors
 at 0.95 or above,
 to avoid some really painful penalties!  The power factor,
 or PF, is simply
 watts divided by volts time amperes.
 
 The issue of power factor is why large Diesel generator
 sets have ratings
 such as 1000 kW/1250 kVAR.  In simple terms, any AC
 generator requires
 torque (engine horsepower) to meet true power demands, and
 excitation (field
 flux intensity) to meet reactive power demands.  When the
 generator load is
 reactive, that is, it has a power factor less than unity,
 the generator must
 not only have the horsepower to supply the energy in watts,
 but it must have
 excess capacity to handle the additional current required
 by motors and
 other low-power-factor loads.  In a nutshell, that is why a
 1000 watt
 generator may be unable to keep running a refrigerator that
 uses only 900
 watts; the fridge may require 1200 VA to operate because it
 has a low power
 factor, and the small generator has no ability to handle
 such loads.
 Because of its relatively small amount of spinning mass,
 such a small
 generator probably could not even handle the
 refrigerator's starting
 current- which is about 5 to 6 times its running current.
 
 73, Eric Lemmon WB6FLY
 
  
 
 -Original Message-
 From: Repeater-Builder@yahoogroups.com
 [mailto:[EMAIL PROTECTED] On Behalf Of
 Albert
 Sent: Tuesday, September 16, 2008 2:13 PM
 To: Repeater-Builder@yahoogroups.com
 Subject: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging
 Power)
 
 Hopefully, you will forgive me for hijacking the post, but
 this brings up a
 question I have had for a long time. What on earth is a
 volt-amp?
 My logic would state that is is the same as a watt, which
 is volts x amps,
 as you probably well know. So what on earth is it?
 
 Confused.
 
 Albert


  


Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread John Barrett
This doesn't mesh up with what I've learned about power factor -- the 
impression that I got was a perfect power factor was 1 (one) (current in 
phase with voltage, equipment using everything the the power company 
charges you for to do useful work). Anything other than PF=1 meant that 
the equipment was using the power less efficiently, and therefore you 
were paying more in KWH than the work actually performed. That 
description excludes the possibly that the equipment could use more 
power than the power company records as being delivered (heck, 
conservation of energy says that in any case). any load reactance 
(inductive or capacitive) and the very low PF numbers stated sound more 
like what I get off my linear power supplies with big capacitance and no 
power factor correction. In any case, anything other than PF=1 should 
mean that you are paying for more power than you are actually using.

Tell me where I goofed this up ??



Bob M. wrote:

 Thank you Eric. This was the explanation I was looking for. The UPS is 
 saving me money when drawing 181 Volt-Amps, yet the electric meter is 
 only recording and charging me for 31 Watts. I wonder if APC did this 
 on purpose. I don't know how much current is actually being fed to the 
 batteries; they've been in there for a couple of months and should be 
 fully charged by now, so it should just be trickling them (eight 12V 
 7A SLA cells in series/parallel for 48V).

 Bob M.
 ==
 --- On Tue, 9/16/08, Eric Lemmon [EMAIL PROTECTED] 
 mailto:wb6fly%40verizon.net wrote:

  From: Eric Lemmon [EMAIL PROTECTED] mailto:wb6fly%40verizon.net
  Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)
  To: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com
  Date: Tuesday, September 16, 2008, 9:21 PM
  Albert,
 
  You are forgiven, because you pose an important question!
 
  The spinning aluminum disk in the kilowatthour meter found
  on most
  residential service-entrance panels measures true power in
  kilowatts versus
  time, which equals energy. Thus, your electric utility
  charges you for the
  true power you use, not for volts times amperes- known as
  reactive power.
  Although the utility must provide the capability to supply
  all of the
  amperes you need, some of those amperes are given
  back to the utility due
  to a lower than unity power factor. That is why many
  utility companies
  charge a kVAR Penalty to certain industrial
  power users whose volt-ampere
  demands far exceed their watt demands, meaning that the
  power factor is low.
  Industrial power users strive to keep their power factors
  at 0.95 or above,
  to avoid some really painful penalties! The power factor,
  or PF, is simply
  watts divided by volts time amperes.
 
  The issue of power factor is why large Diesel generator
  sets have ratings
  such as 1000 kW/1250 kVAR. In simple terms, any AC
  generator requires
  torque (engine horsepower) to meet true power demands, and
  excitation (field
  flux intensity) to meet reactive power demands. When the
  generator load is
  reactive, that is, it has a power factor less than unity,
  the generator must
  not only have the horsepower to supply the energy in watts,
  but it must have
  excess capacity to handle the additional current required
  by motors and
  other low-power-factor loads. In a nutshell, that is why a
  1000 watt
  generator may be unable to keep running a refrigerator that
  uses only 900
  watts; the fridge may require 1200 VA to operate because it
  has a low power
  factor, and the small generator has no ability to handle
  such loads.
  Because of its relatively small amount of spinning mass,
  such a small
  generator probably could not even handle the
  refrigerator's starting
  current- which is about 5 to 6 times its running current.
 
  73, Eric Lemmon WB6FLY
 
 
 
  -Original Message-
  From: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com
  [mailto:Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com] On Behalf Of
  Albert
  Sent: Tuesday, September 16, 2008 2:13 PM
  To: Repeater-Builder@yahoogroups.com 
 mailto:Repeater-Builder%40yahoogroups.com
  Subject: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging
  Power)
 
  Hopefully, you will forgive me for hijacking the post, but
  this brings up a
  question I have had for a long time. What on earth is a
  volt-amp?
  My logic would state that is is the same as a watt, which
  is volts x amps,
  as you probably well know. So what on earth is it?
 
  Confused.
 
  Albert

  


RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread Mark Harrison
Hi Eric,

I agree with most of what you say, except the bit about generators and
horsepower.

I've always understood poor power factor to be a problem because the
generator and distribution system needs to carry higher currents to deliver
the same energy into a poor load.  That's a problem because the power
companies either suffer higher resistive (and financial) losses in their
systems, or they need to use heavier distribution wiring and thicker wires
in their transformers and generators (increasing the infrastructure costs).
To offset these costs they financially discourage anyone from using poor
power factor loads.

It's the same in a generator set.  The difference between the 1,000 Watt/
1250 KVA rating is that with a bad load up to 250 Watts are wasted in
resistive losses in the generator windings, requiring a bit more torque from
the engine to provide the extra 250 Watts and some extra energy to further
cool the generator.

Electronic power supplies, especially older switch modes, cause a whole new
set of problems.  While they show up as poor power factor loads, they also
create harmonics in the supply network, and that could show up on electronic
power meters very inaccurately!

Cheers,
Mark VK3BYY

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Eric Lemmon
Sent: Wednesday, 17 September 2008 11:22 AM
To: Repeater-Builder@yahoogroups.com
Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

Albert,

You are forgiven, because you pose an important question!

The spinning aluminum disk in the kilowatthour meter found on most
residential service-entrance panels measures true power in kilowatts versus
time, which equals energy.  Thus, your electric utility charges you for the
true power you use, not for volts times amperes- known as reactive power.
Although the utility must provide the capability to supply all of the
amperes you need, some of those amperes are given back to the utility due
to a lower than unity power factor.  That is why many utility companies
charge a kVAR Penalty to certain industrial power users whose volt-ampere
demands far exceed their watt demands, meaning that the power factor is low.
Industrial power users strive to keep their power factors at 0.95 or above,
to avoid some really painful penalties!  The power factor, or PF, is simply
watts divided by volts time amperes.

The issue of power factor is why large Diesel generator sets have ratings
such as 1000 kW/1250 kVAR.  In simple terms, any AC generator requires
torque (engine horsepower) to meet true power demands, and excitation (field
flux intensity) to meet reactive power demands.  When the generator load is
reactive, that is, it has a power factor less than unity, the generator must
not only have the horsepower to supply the energy in watts, but it must have
excess capacity to handle the additional current required by motors and
other low-power-factor loads.  In a nutshell, that is why a 1000 watt
generator may be unable to keep running a refrigerator that uses only 900
watts; the fridge may require 1200 VA to operate because it has a low power
factor, and the small generator has no ability to handle such loads.
Because of its relatively small amount of spinning mass, such a small
generator probably could not even handle the refrigerator's starting
current- which is about 5 to 6 times its running current.

73, Eric Lemmon WB6FLY

 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Albert
Sent: Tuesday, September 16, 2008 2:13 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

Hopefully, you will forgive me for hijacking the post, but this brings up a
question I have had for a long time. What on earth is a volt-amp?
My logic would state that is is the same as a watt, which is volts x amps,
as you probably well know. So what on earth is it?

Confused.

Albert






Yahoo! Groups Links





RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread Mark Harrison
Ooops - typo - should have written 1.250 KVA, not 1250KVA as that would mean
1.250 MegaVA !

Mark

-Original Message-
From: Mark Harrison [mailto:[EMAIL PROTECTED] 
Sent: Wednesday, 17 September 2008 2:54 PM
To: 'Repeater-Builder@yahoogroups.com'
Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

Hi Eric,

I agree with most of what you say, except the bit about generators and
horsepower.

I've always understood poor power factor to be a problem because the
generator and distribution system needs to carry higher currents to deliver
the same energy into a poor load.  That's a problem because the power
companies either suffer higher resistive (and financial) losses in their
systems, or they need to use heavier distribution wiring and thicker wires
in their transformers and generators (increasing the infrastructure costs).
To offset these costs they financially discourage anyone from using poor
power factor loads.

It's the same in a generator set.  The difference between the 1,000 Watt/
1250 KVA rating is that with a bad load up to 250 Watts are wasted in
resistive losses in the generator windings, requiring a bit more torque from
the engine to provide the extra 250 Watts and some extra energy to further
cool the generator.

Electronic power supplies, especially older switch modes, cause a whole new
set of problems.  While they show up as poor power factor loads, they also
create harmonics in the supply network, and that could show up on electronic
power meters very inaccurately!

Cheers,
Mark VK3BYY

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Eric Lemmon
Sent: Wednesday, 17 September 2008 11:22 AM
To: Repeater-Builder@yahoogroups.com
Subject: RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

Albert,

You are forgiven, because you pose an important question!

The spinning aluminum disk in the kilowatthour meter found on most
residential service-entrance panels measures true power in kilowatts versus
time, which equals energy.  Thus, your electric utility charges you for the
true power you use, not for volts times amperes- known as reactive power.
Although the utility must provide the capability to supply all of the
amperes you need, some of those amperes are given back to the utility due
to a lower than unity power factor.  That is why many utility companies
charge a kVAR Penalty to certain industrial power users whose volt-ampere
demands far exceed their watt demands, meaning that the power factor is low.
Industrial power users strive to keep their power factors at 0.95 or above,
to avoid some really painful penalties!  The power factor, or PF, is simply
watts divided by volts time amperes.

The issue of power factor is why large Diesel generator sets have ratings
such as 1000 kW/1250 kVAR.  In simple terms, any AC generator requires
torque (engine horsepower) to meet true power demands, and excitation (field
flux intensity) to meet reactive power demands.  When the generator load is
reactive, that is, it has a power factor less than unity, the generator must
not only have the horsepower to supply the energy in watts, but it must have
excess capacity to handle the additional current required by motors and
other low-power-factor loads.  In a nutshell, that is why a 1000 watt
generator may be unable to keep running a refrigerator that uses only 900
watts; the fridge may require 1200 VA to operate because it has a low power
factor, and the small generator has no ability to handle such loads.
Because of its relatively small amount of spinning mass, such a small
generator probably could not even handle the refrigerator's starting
current- which is about 5 to 6 times its running current.

73, Eric Lemmon WB6FLY

 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of Albert
Sent: Tuesday, September 16, 2008 2:13 PM
To: Repeater-Builder@yahoogroups.com
Subject: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

Hopefully, you will forgive me for hijacking the post, but this brings up a
question I have had for a long time. What on earth is a volt-amp?
My logic would state that is is the same as a watt, which is volts x amps,
as you probably well know. So what on earth is it?

Confused.

Albert






Yahoo! Groups Links





RE: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

2008-09-16 Thread Eric Lemmon
John,

You are correct that when the power factor is 1.00, the current is in phase
with the voltage, as it will be in a purely resistive circuit.  In this
unique case, watts equals volt-amperes.  However, when the load is reactive,
the current either leads or lags the applied voltage.  A typical case is a
lightly-loaded induction motor, which may exhibit a power factor around
0.65, which is considered to be a poor PF.  Some of the current drawn by
this motor is used to create torque and perform actual work, and this
current is nearly in phase with the applied voltage.  Some current causes
heating of the copper windings and the field core, and this current is also
nearly in phase with the applied voltage.  Both of these currents consume
true power and are measured in watts.  However, a significant amount of
current does nothing but magnetize the field windings during part of the AC
cycle, and that reactive energy is returned to the source as the magnetic
field collapses just before the field is built up with the opposite polarity
during the other half of the AC cycle.  There are additional reactive
losses, such as eddy-current and hysteresis losses, but the magnetizing
currents are lagging the applied voltage, so they are the cause of apparent
power which is expressed in volt-amperes reactive, also known as VARs.

As was discussed at great length in this forum several months ago, one
cannot measure true power with separate voltage and current meters.  That is
because the readings of separate meters are not synchronized in time.  Even
if one uses two true RMS DVMs to measure voltage and current, one still
winds up with nothing more than apparent power based upon volts times
amperes, or volt-amperes.

To measure true power, one must use an AC power meter that synchronously
measures current and voltage throughout the entire cycle.  This can be
performed by a device called a four-quadrant multiplier which, as its name
implies, performs the multiplication of current and voltage through 360
degrees of phase rotation.  One such instrument is a VIZ Instruments WD-767
Digital Wattmeter, which sold for about $925.  Another device which has
become very popular with Hams is the Kill-A-Watt meter that costs about
$20 from several Internet vendors.  Although not as accurate as the WD-767,
it does perform quite well.

As I stated in an earlier post, the rotating-disk kWH meter on the typical
residence measures only true power.  It does this magic by combining the
magnetic fields of two coils: a voltage coil that is connected in parallel
with the load, and a current coil that is in series with the load.  The
angular displacement of these coil windings is precisely set so that only
currents that are exactly in phase with the voltage result in a torque to
turn the aluminum disk.  A small permanent magnet is placed near the disk so
that the speed of the disk is proportional to the amount of true power being
consumed.  Since speed is movement over time, the disk is geared to a
register that accumulates the number of rotations, which represents power
over time, which is energy.  Thus, the meter measures kilowatthours.  You
pay only for the true power that you actually use; you do not pay for
apparent power since volt-amperes is not true power.

73, Eric Lemmon WB6FLY
 

-Original Message-
From: Repeater-Builder@yahoogroups.com
[mailto:[EMAIL PROTECTED] On Behalf Of John Barrett
Sent: Tuesday, September 16, 2008 9:13 PM
To: Repeater-Builder@yahoogroups.com
Subject: Re: [Repeater-Builder] Volt-Amp (Re: APC UPS Charging Power)

This doesn't mesh up with what I've learned about power factor -- the 
impression that I got was a perfect power factor was 1 (one) (current in 
phase with voltage, equipment using everything the the power company 
charges you for to do useful work). Anything other than PF=1 meant that 
the equipment was using the power less efficiently, and therefore you 
were paying more in KWH than the work actually performed. That 
description excludes the possibly that the equipment could use more 
power than the power company records as being delivered (heck, 
conservation of energy says that in any case). any load reactance 
(inductive or capacitive) and the very low PF numbers stated sound more 
like what I get off my linear power supplies with big capacitance and no 
power factor correction. In any case, anything other than PF=1 should 
mean that you are paying for more power than you are actually using.

Tell me where I goofed this up ??

Bob M. wrote:

 Thank you Eric. This was the explanation I was looking for. The UPS is 
 saving me money when drawing 181 Volt-Amps, yet the electric meter is 
 only recording and charging me for 31 Watts. I wonder if APC did this 
 on purpose. I don't know how much current is actually being fed to the 
 batteries; they've been in there for a couple of months and should be 
 fully charged by now, so it should just be trickling them (eight 12V 
 7A SLA cells in series