@mailman.qth.net
Subject: Re: [Elecraft] 240V Line
Message-ID: 54a20a1e.20...@mesanetworks.net
Content-Type: text/plain; charset=utf-8; format=flowed
What Jim says here is correct.
The old exception that allowed returning 120V loads to the bare or green
grounding wire of a 240V circuit was very limited
On Tue,12/30/2014 12:01 AM, Edward R Cole wrote:
I concur. As result of this discussion and because I will soon add
another 240vac outlet to serve my 50v-50a switching PS being installed
to power a 1100w surplus ch.2 TV Harris amplifier (for use on 6m), I
looked closely at some of the
On 12/30/2014 9:35 AM, Jim Brown wrote:
In general, the ground conductor must be sized at least equal to the
phase conductors.
I was always under the impression that the ground wire must be sized for
the circuit overcurrent rating (i.e. breaker/fuse rating). I have on
several occasions
I'm not an electrician, but I am currently having my house wiring
re-done by an electrician and this is my understanding:
If you want to run 220V and 110V outlets from the same breaker, you need
to use a sub-panel with separate breakers for the 110V circuits. Four
wires are needed from the
Folks - Let's close this thread for now to reduce list SNR due to the large
volume of posts.
In the future, please also refrain from using ALL CAPS and ! in emails, as
those are interpreted as shouting and are not appropriate for this list.
73,
Eric
elecraft.com
On 12/30/2014 9:35 AM,
What Jim says here is correct.
The old exception that allowed returning 120V loads to the bare or green
grounding wire of a 240V circuit was very limited, allowed only for a
few large appliances (dryers, stoves/ovens, and water heaters IIRC)
which would be disconnected only for maintenance or
In retrospect, its better if you contract a licensed electrician to
run 240v wiring as his license is at risk and is liable if codes are
violated. If you are not sure of the code and regulations, then I
would say don't DIY.
I am lucky as there is no zoning or covenants where I live.
Installing a 240V outlet is not a big deal unless the construction of
your home makes it difficult to run the cable. Barring that, a competent
electrician should be able to do that in a half day; a difficult run
could double the work. All that is required is a pair plus a Green wire.
If you
On 12/24/2014 10:39 AM, Jim Brown wrote:
Installing a 240V outlet is not a big deal unless the construction of
your home makes it difficult to run the cable. Barring that, a competent
electrician should be able to do that in a half day; a difficult run
could double the work. All that is
On Wed, Dec 24, 2014 at 2:13 PM, Phil Kane k2...@kanafi.org wrote:
On 12/24/2014 10:39 AM, Jim Brown wrote:
Installing a 240V outlet is not a big deal unless the construction of
your home makes it difficult to run the cable. Barring that, a competent
electrician should be able to do that
On Wed,12/24/2014 11:41 AM, Charlie T, K3ICH wrote:
A lot of the older amps (Thunderbolt for example) had 120 V fans wired
from one hot to ground. I always wondered about that.
I think that used to be legal, but it is no longer, and it's very bad
practice.
The better ones (Ten Tec Titan,
Electric ranges used to have a 110 VAC outlet in which the ground and
neutral were wired together. (The 220V plug had only three prongs.) I
always wondered how they got away with that.
Alan N1AL
On 12/24/2014 01:50 PM, Jim Brown wrote:
On Wed,12/24/2014 11:41 AM, Charlie T, K3ICH wrote:
A
] 240V Line
On Wed,12/24/2014 11:41 AM, Charlie T, K3ICH wrote:
A lot of the older amps (Thunderbolt for example) had 120 V fans wired
from one hot to ground. I always wondered about that.
I think that used to be legal, but it is no longer, and it's very bad
practice.
The better ones (Ten Tec