Travis-
Make sense, thank you. This is the first time I’ve ran across this.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Travis Mack <t.m...@mepcad.com>
Sent: Wednesday, July 12, 2023 3:49 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

If this is a wall “hydrant”, then it is outside.  So, I would put my outside 
hose there.  You want this as a separate line taken from the supply side of 
your system control valve.  How would you supply a hydrant that was to be 
located in the front of the building.  It would come off before your system 
control valve.  This is no different than if it comes off the underground or if 
you have to run the piping through the building.  You want the “hydrant” to be 
live, even if the sprinkler system is shut down for maintenance.

Again, don’t over complicate it.  Just think of how you would do a hydrant.  
Just find out if the AHJ wants it treated as a manual standpipe or if he wants 
it as a hydrant.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 12:30 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Skyler-
I can’t find a clear answer to where I need to tie this in. I’ve seen it needs 
to be its own stand-alone line right off the supply entering the building an 
I’ve also seen it coming off one of the FP system Mains. Any thoughts?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Skyler Bilbo <sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>>
Sent: Wednesday, July 12, 2023 3:23 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Everyone already covered the difference between a wall hydrant and FDC, so I 
won't keep doing that.  I have had a similar situation, adding a wall hydrant, 
and I'm curious if the standards would require outside or inside hose demand to 
be added to the fire sprinkler system calcs at the new connection location?  It 
makes sense to me that it would be your outside hose demand, but I would love 
to be wrong.


Thanks,
Skyler Bilbo
[https://ci3.googleusercontent.com/mail-sig/AIorK4y8Hq3kJpcrMKcZPAe4JT4xB7a2Rf10HH9h91m15sYft0q0IkyUaWivqrU3_iQPJ9vznaW8t_4]
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax

sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>
www.wenteplumbing.com<http://www.wenteplumbing.com>


On Wed, Jul 12, 2023 at 1:45 PM Brian Harris 
<bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>> wrote:
Ryan-
Is there some type of schematic available for this? Control valve, check valve, 
etc.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: Hinson, Ryan <rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>>
Sent: Wednesday, July 12, 2023 2:35 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

As has been said by others.  This is not an FDC and would result in monitoring 
issues within the building.  What they are looking for is a wall hydrant which 
needs to be connected to the lead-in upstream of any building suppression 
systems.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.burnsmcd.com%2f&c=E,1,hOx_yuZwpCKr6sZK2CE5KVD5A_hqHxBkBunZ62abgzzwFOPaJR60ypsKli4nQLt44lG_ruvcNjaF4fdDZ_h4geNFdUMTueRJ5YPUHKJprOQV&typo=1>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 1:29 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Ryan-
Yes. They want to draw water from inside the building FP system to use in fore 
hoses for outside the building. “It’s cheaper than adding a hydrant….”

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,s_r7hpBPpQl2BWjo-Mvo5uQJvSyOjNBJyHxvrRQdYO0I4sKzgubiSBlLcoMjWkWrVeMfu8n2Kvjhh10c-h4pvliQmJgiVDWkri2NmlmmY3nMQw,,&typo=1>


From: Hinson, Ryan <rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>>
Sent: Wednesday, July 12, 2023 2:25 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

FDC…as in injection into the system on the back side in the absence of fire 
hydrants nearby doesn’t make sense to me.  Do you mean to draw water off the FW 
piping in the building to serve portable equipment for the parking lot storage?

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
rhin...@burnsmcd.com<mailto:rhin...@burnsmcd.com>  \  
burnsmcd.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.burnsmcd.com%2f&c=E,1,7VFuIwuxPjOttrVgynPolVOTgN3v6mT-V6g87jq-Q2EvwrY7AAFdS1ToF0kt5EBG9OYlkVkYa2frZoY5Yh2qLTkFn5Iw7WH7j4mnGlxT9GuOLxsUbhhdyw,,&typo=1>
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> 
<matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>>
Sent: Wednesday, July 12, 2023 1:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Nope. Exterior fire operations are as or more important than internal.

Seen this many times for different applications.

R/
Matt

Please rate our customer 
service<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fsurvey.medallia.com%2f%3femailsignature%26fc%3d3539%26bg%3dFire%2520and%2520Fabrication&c=E,1,srwSq8YdVmazH4zsAgasid0nRVIUZrVEzSqa9212B7ULLYAOtDti9oRFL0FjT0h5WKOorJZ6qJIa5p6Gp_6TcG1lKeSP72YRuaYIZwVkZ_cXaQPdrmPfCLoFFjZa&typo=1>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.fergusonfire.com%2f&c=E,1,t2kkU6GiN48ipjo2cUguayf2olg-9ggZNBHGg4GIUPquGYTwa57Bsl6HIod0TTUnlD6KAmZOf15WFvAedioRCYUOHkT_leEbTXykFA5lKZCQPB2yTNYoJIyI&typo=1>

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 2:19 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] 2nd FDC Instead of a Hydrant ???

This is a first. We recently did a sprinkler system for a 2-story storage 
building. The owner is now putting storage containers in the back parking lot 
and the AHJ wants him to add a 2nd FDC on the back of the building, there’s 
already one on the front, and use it to “supply” fire hoses if there’s a fire 
outside since there’s not a hydrant in the back…. Tell me I’m crazy.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,KvUcJKwR1-VMeJ08pas56fB1FbmRf44mocNWawMpPEDp7swm7LB7aN-PQwe7ORb0mBUyEoXrzXuPAFliI6m20_hR6VaomNnzFc--WU3fuFARFdI,&typo=1>
Phone: 704.896.9989
Fax: 704.896.1935



_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
sprinklerforum-le...@lists.firesprinkler.org<mailto:sprinklerforum-le...@lists.firesprinkler.org>