Pretty good supply if you can flow 1800 gpm at a good pressure without a pump. 
  
  
  
  
  
  
  
  

  
  
>   
> On Jul 12, 2023 at 4:37 PM,  <Craig Prahl (mailto:craig.pr...@jacobs.com)>  
> wrote:
>   
>   
>         
>   
>
> Providing an array of 2.5” hose valves as a test header for testing the 
> backflow preventer.    Sprinkler System demand is around 1800 gpm.
>
>   
>
>   
>
>   
>
> So, here’s the debate, when determining how many valves you need do you 
> consider each valve capable of 250 gpm or 500 gpm flow?
>
>   
>
>   
>
>   
>
> Nothing in NFPA 13, the debate goes on………….
>
>   
>
>   
>
>   
>
>  Craig Prahl   |Jacobs     | Fire Protection SME – Special Hazards |    
> craig.pr...@jacobs.com (mailto:craig.pr...@jacobs.com)|www.jacobs.com 
> (https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$)
>
>   
>
> 1041 East Butler Road      Greenville, South Carolina    29606
>
>   
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>   
>
>   
>
>   
>   
>     
>  NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to