Well, it is a connection point for the fire department.  So technically it is 
an FDC.  However, you just need to understand that he wants to be able to draft 
water from that connection.  So, you will need to give him an outlet.  If you 
google "fire protection wall hydrant" you should be able to find plenty of 
images of what you need.

Be sure to check what flows and pressures the AHJ wants so you can calculate to 
provide that.  As Zach stated, many times they are treated as just a manual 
standpipe.  Others, in my experience, have treated them as hydrants and we had 
to provide site fire flow demands.


Travis Mack, SET
M.E.P.CAD |
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 11:37 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Matt-
I'm just regurgitating what the AHJ is saying. I think that's where the 
confusion is coming from.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> 
<matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>>
Sent: Wednesday, July 12, 2023 2:32 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

I think you are saying FDC, what I heard from the description is wall hydrant.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 2:27 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Matt-
So your saying it's ok to do? There's (2) systems fed off the front Riser so 
the FDC ties in there. What do you do for the "extra" FDC? Tie it off the back 
Main?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>


From: matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com> 
<matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>>
Sent: Wednesday, July 12, 2023 2:22 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Re: 2nd FDC Instead of a Hydrant ???

Nope. Exterior fire operations are as or more important than internal.

Seen this many times for different applications.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
matthew.will...@ferguson.com<mailto:matthew.will...@ferguson.com>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Brian Harris <bhar...@bvssystemsinc.com<mailto:bhar...@bvssystemsinc.com>>
Sent: Wednesday, July 12, 2023 2:19 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] 2nd FDC Instead of a Hydrant ???

This is a first. We recently did a sprinkler system for a 2-story storage 
building. The owner is now putting storage containers in the back parking lot 
and the AHJ wants him to add a 2nd FDC on the back of the building, there's 
already one on the front, and use it to "supply" fire hoses if there's a fire 
outside since there's not a hydrant in the back.... Tell me I'm crazy.

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to