Todd,
As a retired AHJ, my opinion would be that you do not need the hose valves on 
the first-floor standpipe risers for fighting a fire on the first floor, since 
access to the first floor is not gained through the stairwells.
However, you'd need to pass that by the fire chief of the department 
responsible for providing that service, and the permitting authority for the 
installation for approval. One of the last things that you want to do is create 
a condition that is not expected by the fire department, so such an arrangement 
needs to be incorporated into the building preplan.
As a firefighter, I would expect that hose outlet to be there (on the first 
floor in the stairwell).  We use it for fighting fires on the second floor, and 
as an alternate method of supplying the standpipes if for some reason the fire 
department connection is dysfunctional.

 
 
 I am working on a small 4 story building where we are required to install a 
standpipe (as well as a full 13 sprinkler system). The first floor consists of 
a conference area, office space and various mechanical and storage rooms. The 
conference space and office area have direct access to the outside, but there 
is no communicating space between them. The 2 stairways lead to an outside 
access only. The elevator lobby has an outside door but does not connect to the 
stairways or conference and office spaces. The total footprint of the building 
is less than 3000 sqft. 
Where do you put the hose valve on the 1st floor?
Todd G Williams, PEFire Protection Design/ConsultingStonington, CT860-535-2080 
(ofc)860-554-7054  (fax)860-608-4559 (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org  
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to