Steve, a quick search found a couple of different MSDS. The older ones showed 
as you said but some newer ones called it a IIIB flammable liquid. I would 
suggest contact the supplier and get the latest MSDS.   
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Apr 12, 2024 at 2:59 PM,  <Steve Leyton 
> (mailto:st...@protectiondesign.com)>  wrote:
>   
>   
>           
>   
>
> Happy Friday Forumites:
>   
>  I’m doing an assessment for a client who’s being compelled to upgrade their 
> DCDA to an RPDA in an area that is served by a public water system zone that 
> has dropped significantly in working pressure since the time the subject 
> building was certified for occupancy.      Typically in this scenario, the 
> City of San Diego requires that you prove that the residual pressure and flow 
> on the calc’ card can still be met after additional pressure loss is taken 
> for the RP device, but in this case it cannot.      So we’re looking at it 
> from a protect-to-suit standpoint so that the owner and tenants can at least 
> maintain ongoing operations.    Ran into a fishing lure manufacturer in one 
> of the suites and they make swim baits from Plastisol, which is essentially 
> liquid PVC, 60-100% depending on application.         The fire and ignition 
> info on a standard form MSDS states “Not applicable” for the metrics we use 
> to evaluate flammable liquid class, so I’m wondering if anyone has experience 
> classifying this liquid (there are 9x 55 gallon drums in the suite) and what 
> the flash point and commodity classification might be once it’s been baked 
> into fake sardines and whatnot?      I’m assuming its Group A since it’s PVC 
> and semi-solid at that point.     
>
>   
>
>   
>
>   
>
>   
>
>   
>
>
>
>   
>
>    Steve Leyton, President
>  T    |   619.255.8964 x 102      |       www.protectiondesign.com 
> (http://www.protectiondesign.com/)
>   2851 Camino Del Rio South      |    Suite 210      |    San Diego, CA    
> 92108
> Fire Protection System Design    |    Consulting    |    Planning    |    
> Training
>
>   
>
>   
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to