Not a problem, Bob. That came from the “Learn from experience” department.   
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On May 6, 2024 at 8:38 PM,  <Bob Knight (mailto:b...@firebyknight.com)>  
> wrote:
>   
>   
>   As a follow up to this, I ran the calcs both with an adjusted pressure and 
> by creating the fictitious underground.
>  The made up underground with the fire pump as the source created a lower 
> overall demand.
>  So, I'm more comfortable using the adjusted water pressure for the calcs.    
> When a final set of utility plans is made available the calcs will be 
> adjusted accordingly.    At this point I like the idea of going with the more 
> stringent of the two ideas.
>   
>  I appreciate all the help, and thanks Todd for pointing out the obvious fact 
> that I missed about the static pressure.   
>   
>   
>   
>   
> Thank you,
>  Bob Knight, CET III
>   Fire by Knight, LLC
>   208-318-3057
>         
> On 5/6/2024 3:18 PM, Fpdcdesign wrote:
>   
> >     
> > There is no friction loss at 0 gpm. The static at the riser will be your 
> > churn pressure plus the elevation gain.   
> >   
> >
> >  In my opinion, you should include the mains as you describe them as part 
> > of the calculation.     
> >
> >   
> >   
> >   
> > Todd Williams     
> > Fire Protection Design/Consulting
> >   
> > Stonington, CT
> >   
> > 860-608-4559
> >   
> >   
> >   
> >   
> >   
> >
> >   
> >   
> > >   
> > > On May 6, 2024 at 4:57 PM,  <Bob Knight (mailto:b...@firebyknight.com)>  
> > > wrote:
> > >   
> > >   
> > >   I have a project where the complete underground plan has not been 
> > > provided, yet.
> > >  What I do have is a fire pump house with a recent fire pump test.
> > >  The fire pump house is about 2,100 feet from the project site.    It is 
> > > elevated about 54 feet higher as well.
> > >  I do have the underground loop around the building, so I was going to 
> > > use the connection point at the loop for the underground from the pump 
> > > house as the source point.
> > >  The pump test shows 152 psi @ 0 gpm and 101 psi @ 1500 gpm.
> > >  The elevation gain in pressure is 23.38 psi.
> > >  The friction loss through the 2,100 feet of pipe and 16 or so fittings 
> > > and valves, totals 2,372 feet.
> > >  This came out to 21.24 psi of friction loss, assuming 800 gpm of flow 
> > > including 250 gpm hose.
> > >  I'm adding the elevation gain and subtracting the friction loss from the 
> > > pump test.
> > >  This leaves me with 154.14 psi @ 0 gpm and 103.14 psi @ 1500 gpm.
> > >  I'm just going to use the numbers from the pump test and re-verify 
> > > everything at a future date.
> > >  Does this sound reasonable?
> > >   
> > >   
> > > --
> > >   
> > >   
> > >   
> > > Thank you,
> > >  Bob Knight, CET III
> > >   Fire by Knight, LLC
> > >   208-318-3057
> > >         
> > >
> > >   
> > >   
> > >   
> > >   
> > >
> > >   
> > >  Virus-free.www.avg.com 
> > > (http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient)
> > >   
> > >   
> > >   
> > >   
> > >  _________________________________________________________ SprinklerForum 
> > > mailing list:   
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >   To unsubscribe send an email to  
> > > sprinklerforum-le...@lists.firesprinkler.org 
> > > (mailto:sprinklerforum-le...@lists.firesprinkler.org)
> > >   
> >   
> >   
> >   
> >   
> >     
> >  _________________________________________________________ SprinklerForum 
> > mailing list:  
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> >  To unsubscribe send an email to  
> > sprinklerforum-le...@lists.firesprinkler.org 
> > (mailto:sprinklerforum-le...@lists.firesprinkler.org)   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to sprinklerforum-le...@lists.firesprinkler.org

Reply via email to