APC charger is calibrated for AGM, doesn’t flooded require different voltages?  
Maybe I’m wrong about that.  Certainly take out the internal AGM batteries, you 
don’t want batteries of different chemistry in parallel.  I’ve only done it 
with external AGM, but as far as how you get to the right voltage (I forget if 
2200 VA is still 24V or that’s the point where they started using 48V), I don’t 
think it matters if you put 2 x 12V or 4 x 6V in series to get 24V.  I’m not 
sure you’ll find 24 or 48V batteries, the choices are usually 2, 6 or 12 volt.  
Make sure to put a fuse in each series string of batteries.

From: Josh Luthman 
Sent: Tuesday, January 20, 2015 2:50 PM
To: [email protected] 
Subject: Re: [AFMUG] Bigger batteries for Smart UPS

Charger but also just an APC with the management.  So far I've got two 
solutions: DC and APC.  I'd rather avoid another model or method to monitor.

Should I just load up on some decent size wet cell and wire them up?

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Jan 20, 2015 3:32 PM, "Ken Hohhof" <[email protected]> wrote:

  I don’t have specific numbers for you, but I have observed that family gets 
pretty inefficient if you run it way below rated capacity.  You seem to hit a 
wall as you drop the load, like 200 watts for 4 hours, 100 watts for 4 hours, 
50 watts for 4 hours, no watts for 4 hours.  Especially if you are trying to 
push the runtime out to days.

  Any reason you are using a 2200 VA unit for only 70W?  Instead of, say, a 700 
VA unit?  Wanting the faster charger?


  From: Josh Luthman 
  Sent: Tuesday, January 20, 2015 2:14 PM
  To: [email protected] 
  Subject: [AFMUG] Bigger batteries for Smart UPS

  I'm getting a bigger unit - SmartUPS XL 2200 - and I'm looking at batteries.  
I have an Interstate Batteries and Batteries Plus near me so I'd like to go 
with either of them. 

  This will be indoors.  I'm aiming to get 280 watt hours (70 watts, 4 hours) 
of run time.  Is there any idea as to the inefficiency of the whole AC/DC/AC/DC 
process?

  What type of battery would be best?  Should I look for 12/24/48v batteries or 
does it matter (besides having to connect them in series)?


  Josh Luthman
  Office: 937-552-2340
  Direct: 937-552-2343
  1100 Wayne St
  Suite 1337
  Troy, OH 45373