Excellent info.  Thanks Bill!!

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Tue, Jan 20, 2015 at 7:50 PM, Bill Prince <[email protected]> wrote:

> I generally figure about 10% loss for each conversion.  Some inverters and
> some power supplies will be better and/or worse.
>
> So converting from DC to AC, you have roughly 90% of what you started
> with.  Going from AC to DC you'll end up with 80% of what you started with.
>
> If you want 70 watts for 4 hours, or 280 watt hours, you will need ~~ 560
> watt hours of battery for a DC solution.  That roughly equates to 700 watt
> hours for a UPS solution.
>
> If you're using 12 volt batteries, your UPS could use anything over 60 AH
> per battery.
>
> If you go with DC-only, you could get by with 47 AH per battery.
>
> Your best battery choice is AGM.  They can be discharged deeper than most
> of the other types (gel, wet).
>
> bp
> <part15sbs{at}gmail{dot}com>
>
>
> On 1/20/2015 3:50 PM, Josh Luthman wrote:
>
>> This will be indoors.  I'm aiming to get 280 watt hours (70 watts, 4
>> hours) of run time.  Is there any idea as to the inefficiency of the whole
>> AC/DC/AC/DC process?
>>
>
>