70 watt load.  I'd like to get 4 hours.  280 watt hours.

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373
On Jan 20, 2015 4:25 PM, "Gino Villarini" <[email protected]> wrote:

>  The 2200 is 48vdc iirc, for a 289 watt load It will be inefficient...
> Better off with a 750xl
>
> Gino A. Villarini
> @gvillarini
>
>
>
> On Jan 20, 2015, at 5:17 PM, Ken Hohhof <[email protected]> wrote:
>
>    APC charger is calibrated for AGM, doesn’t flooded require different
> voltages?  Maybe I’m wrong about that.  Certainly take out the internal AGM
> batteries, you don’t want batteries of different chemistry in parallel.
> I’ve only done it with external AGM, but as far as how you get to the right
> voltage (I forget if 2200 VA is still 24V or that’s the point where they
> started using 48V), I don’t think it matters if you put 2 x 12V or 4 x 6V
> in series to get 24V.  I’m not sure you’ll find 24 or 48V batteries, the
> choices are usually 2, 6 or 12 volt.  Make sure to put a fuse in each
> series string of batteries.
>
>  *From:* Josh Luthman <[email protected]>
> *Sent:* Tuesday, January 20, 2015 2:50 PM
> *To:* [email protected]
> *Subject:* Re: [AFMUG] Bigger batteries for Smart UPS
>
>
> Charger but also just an APC with the management.  So far I've got two
> solutions: DC and APC.  I'd rather avoid another model or method to monitor.
>
> Should I just load up on some decent size wet cell and wire them up?
>
> Josh Luthman
> Office: 937-552-2340
> Direct: 937-552-2343
> 1100 Wayne St
> Suite 1337
> Troy, OH 45373
> On Jan 20, 2015 3:32 PM, "Ken Hohhof" <[email protected]> wrote:
>
>>   I don’t have specific numbers for you, but I have observed that family
>> gets pretty inefficient if you run it way below rated capacity.  You seem
>> to hit a wall as you drop the load, like 200 watts for 4 hours, 100 watts
>> for 4 hours, 50 watts for 4 hours, no watts for 4 hours.  Especially if you
>> are trying to push the runtime out to days.
>>
>> Any reason you are using a 2200 VA unit for only 70W?  Instead of, say, a
>> 700 VA unit?  Wanting the faster charger?
>>
>>
>>  *From:* Josh Luthman <[email protected]>
>> *Sent:* Tuesday, January 20, 2015 2:14 PM
>> *To:* [email protected]
>> *Subject:* [AFMUG] Bigger batteries for Smart UPS
>>
>>  I'm getting a bigger unit - SmartUPS XL 2200 - and I'm looking at
>> batteries.  I have an Interstate Batteries and Batteries Plus near me so
>> I'd like to go with either of them.
>>
>> This will be indoors.  I'm aiming to get 280 watt hours (70 watts, 4
>> hours) of run time.  Is there any idea as to the inefficiency of the whole
>> AC/DC/AC/DC process?
>>
>> What type of battery would be best?  Should I look for 12/24/48v
>> batteries or does it matter (besides having to connect them in series)?
>>
>> Josh Luthman
>> Office: 937-552-2340
>> Direct: 937-552-2343
>> 1100 Wayne St
>> Suite 1337
>> Troy, OH 45373
>>
>

Reply via email to