Sine wave would be 60 hz.  Not the voltage.

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373
On Apr 8, 2015 10:35 PM, "George Skorup (Cyber Broadcasting)" <
[email protected]> wrote:

>  I want to say the Honda's and Yamaha's use a pure since wave inverter.
> Our Yamaha is definitely stable, ~120-122 volts solid. Even UPS's set to
> high sensitivity don't complain. It is worth the extra couple hundred $ for
> a good inverter generator.
>
> On 4/8/2015 9:13 PM, Forrest Christian (List Account) wrote:
>
> The difference between an inverter and a non inverter generator is that
> the non inverter models typically use an ac generator which directly
> produces ac power.  This requires the motor to be running at the correct
> rpm to get the proper ac frequency.  In addition, they tend to be
> susceptible to sags and surges because the motor itself has to be throttled
> up or down based on load.
>
> The inverter units usually use a dc generator tied to an ac inverter.
> This solves the problems described above but then you're at the mercy of
> the quality of the inverter, which can vary greatly.
>  On Apr 8, 2015 6:40 PM, "Josh Luthman" <[email protected]>
> wrote:
>
>> So for example this:
>>
>> http://www.autozone.com/power-tools/portable-generator/power-pro-1000-watt-generator-no-return-on-used-generator-/290845_0_0/
>>
>>  It has a 120v outlet but doesn't have an inverter.  How is that
>> possible?
>>
>>  This is $320 and says inverter:
>>
>> http://www.autozone.com/power-tools/portable-generator/generac-portable-inverter-generator/568401_0_0/
>>
>>  The big ones I have definitely work on the big APCs (1500-2200va).  I
>> bought them in 2008? so I don't have the specs anymore.
>>
>>  The site's I'd be most likely to use it would be going into a Meanwell
>> rectifier.
>>
>>
>>  Josh Luthman
>> Office: 937-552-2340
>> Direct: 937-552-2343
>> 1100 Wayne St
>> Suite 1337
>> Troy, OH 45373
>>
>> On Wed, Apr 8, 2015 at 8:33 PM, Glen Waldrop <[email protected]>
>> wrote:
>>
>>>  I'm not sure how picky your hardware is, but most inverters and
>>> generators don't put out a full sine wave. Battery backups tend to trip
>>> constantly, but my equipment seems to handle it fine.
>>>
>>> Full sine wave generators tend to cost a little bit more.
>>>
>>>
>>>
>>> ----- Original Message -----
>>> *From:* Josh Luthman <[email protected]>
>>> *To:* [email protected]
>>> *Sent:* Wednesday, April 08, 2015 7:21 PM
>>> *Subject:* [AFMUG] Smaller generators with inverters
>>>
>>>  Can anyone share what kind of generators they're using?  I'm looking
>>> for something that's smaller for one person to carry.  I don't need
>>> anything big, maybe 250 watt load at the most.  Looking online I see $600
>>> minimum.  I'd be using this at smaller sites that don't already have a big
>>> 24 hour generator already so portability would be the most important
>>> feature.
>>>
>>>  Josh Luthman
>>> Office: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>>
>>
>

Reply via email to