Alpha requires 4U for 8kW: 125/220Vdc Cordex 4.4kW

On Fri, Jul 15, 2016 at 10:13 AM, Eric Kuhnke <eric.kuh...@gmail.com> wrote:

>  I need way more than 2000W, the Eltek unit pictured is 4 x 2000W
> rectifiers running in parallel, nominally 8kW if running form a 240VAC
> input source. Somewhat less on 208V.
>
> On Fri, Jul 15, 2016 at 7:06 AM, can...@believewireless.net <
> p...@believewireless.net> wrote:
>
>> For the distribution bus, we use ICT. It's 1U and they have a version
>> that support two inputs in 1U.
>> It allows you to power cycle your loads. You can connect it to the
>> rectifier of your choice.
>> We get these from Winncom.
>>
>> If you don't need the full 2000W, Alpha makes a 2U 48Vdc Cordex HP 1.2kW
>> 2RU
>> ā€‹. But you can't
>> power cycle the loads.ā€‹ You can order these direct or from Winncom/Tessco.
>>
>> .
>>
>> On Thu, Jul 14, 2016 at 9:34 PM, Eric Kuhnke <eric.kuh...@gmail.com>
>> wrote:
>>
>>> Looked, but the original FlatPack is not dense enough, the FlatPack2 and
>>> HE models are much smaller...  I am figuring out if a design for a POP will
>>> fit in a single 45U rack with A and B power, each rectifier setup needs to
>>> be 3U to 4U height maximum.
>>>
>>> On Thu, Jul 14, 2016 at 10:52 AM, Peter Kranz <pkr...@unwiredltd.com>
>>> wrote:
>>>
>>>> Iā€™d give ebay a scan, usually there are a few flatpack units there..
>>>>
>>>>
>>>>
>>>>
>>>> *Peter Kranz*www.UnwiredLtd.com <http://www.unwiredltd.com/>
>>>> Desk: 510-868-1614 x100
>>>> Mobile: 510-207-0000
>>>> pkr...@unwiredltd.com
>>>>
>>>>
>>>>
>>>> *From:* Af [mailto:af-boun...@afmug.com] *On Behalf Of *Eric Kuhnke
>>>> *Sent:* Monday, July 11, 2016 4:10 PM
>>>> *To:* af@afmug.com
>>>> *Subject:* [AFMUG] Anyone purchased an Eltek rectifier system recently?
>>>>
>>>>
>>>>
>>>> Looking for a ballpark price estimate off list on this:
>>>>
>>>>
>>>> http://www.eltek.com/detail_products.epl?id=1142848&cat=24677&k1=&k2=&k3=&k4=&close=1
>>>>
>>>> It has a distribution bus/fuse/breaker panel in the top 1U, the bottom
>>>> 1U populated with 4 x 2000W rectifiers.
>>>>
>>>> Or something else equivalent that is 2U to max 3U in size, 8kW rated at
>>>> 230/240VAC input.
>>>>
>>>>
>>>
>>
>

Reply via email to