I've only used their 2U shelves in 24V and -48V in 110V applicatons. So I'm
not familiar with their 1U shelves.

On Fri, Jul 15, 2016 at 10:34 AM, Eric Kuhnke <[email protected]> wrote:

> The closest Alpha equivalent to the Flatpack2 HE seems to be:
>
>
> http://www.alpha.com/index.php/products-mobile/cable-tv-broadband-products/item/48vdc-cordex-hp-24kw?category_id=440
>
>
> http://tools.alpha.ca/library/showdocs.asp?PId=00000000000039F7&type=b&salp=1
>
> Which is actually more power dense, 4 x 2.4 kW in 1U for just the
> rectifier shelf (no distribution).
>
>
>
> On Fri, Jul 15, 2016 at 7:29 AM, [email protected] <
> [email protected]> wrote:
>
>> Alpha requires 4U for 8kW: 125/220Vdc Cordex 4.4kW
>>
>>
>> On Fri, Jul 15, 2016 at 10:13 AM, Eric Kuhnke <[email protected]>
>> wrote:
>>
>>>  I need way more than 2000W, the Eltek unit pictured is 4 x 2000W
>>> rectifiers running in parallel, nominally 8kW if running form a 240VAC
>>> input source. Somewhat less on 208V.
>>>
>>> On Fri, Jul 15, 2016 at 7:06 AM, [email protected] <
>>> [email protected]> wrote:
>>>
>>>> For the distribution bus, we use ICT. It's 1U and they have a version
>>>> that support two inputs in 1U.
>>>> It allows you to power cycle your loads. You can connect it to the
>>>> rectifier of your choice.
>>>> We get these from Winncom.
>>>>
>>>> If you don't need the full 2000W, Alpha makes a 2U 48Vdc Cordex HP
>>>> 1.2kW 2RU
>>>> ​. But you can't
>>>> power cycle the loads.​ You can order these direct or from
>>>> Winncom/Tessco.
>>>>
>>>> .
>>>>
>>>> On Thu, Jul 14, 2016 at 9:34 PM, Eric Kuhnke <[email protected]>
>>>> wrote:
>>>>
>>>>> Looked, but the original FlatPack is not dense enough, the FlatPack2
>>>>> and HE models are much smaller...  I am figuring out if a design for a POP
>>>>> will fit in a single 45U rack with A and B power, each rectifier setup
>>>>> needs to be 3U to 4U height maximum.
>>>>>
>>>>> On Thu, Jul 14, 2016 at 10:52 AM, Peter Kranz <[email protected]>
>>>>> wrote:
>>>>>
>>>>>> I’d give ebay a scan, usually there are a few flatpack units there..
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> *Peter Kranz*www.UnwiredLtd.com <http://www.unwiredltd.com/>
>>>>>> Desk: 510-868-1614 x100
>>>>>> Mobile: 510-207-0000
>>>>>> [email protected]
>>>>>>
>>>>>>
>>>>>>
>>>>>> *From:* Af [mailto:[email protected]] *On Behalf Of *Eric Kuhnke
>>>>>> *Sent:* Monday, July 11, 2016 4:10 PM
>>>>>> *To:* [email protected]
>>>>>> *Subject:* [AFMUG] Anyone purchased an Eltek rectifier system
>>>>>> recently?
>>>>>>
>>>>>>
>>>>>>
>>>>>> Looking for a ballpark price estimate off list on this:
>>>>>>
>>>>>>
>>>>>> http://www.eltek.com/detail_products.epl?id=1142848&cat=24677&k1=&k2=&k3=&k4=&close=1
>>>>>>
>>>>>> It has a distribution bus/fuse/breaker panel in the top 1U, the
>>>>>> bottom 1U populated with 4 x 2000W rectifiers.
>>>>>>
>>>>>> Or something else equivalent that is 2U to max 3U in size, 8kW rated
>>>>>> at 230/240VAC input.
>>>>>>
>>>>>>
>>>>>
>>>>
>>>
>>
>

Reply via email to