The closest Alpha equivalent to the Flatpack2 HE seems to be:

http://www.alpha.com/index.php/products-mobile/cable-tv-broadband-products/item/48vdc-cordex-hp-24kw?category_id=440

http://tools.alpha.ca/library/showdocs.asp?PId=00000000000039F7&type=b&salp=1

Which is actually more power dense, 4 x 2.4 kW in 1U for just the rectifier
shelf (no distribution).



On Fri, Jul 15, 2016 at 7:29 AM, [email protected] <
[email protected]> wrote:

> Alpha requires 4U for 8kW: 125/220Vdc Cordex 4.4kW
>
>
> On Fri, Jul 15, 2016 at 10:13 AM, Eric Kuhnke <[email protected]>
> wrote:
>
>>  I need way more than 2000W, the Eltek unit pictured is 4 x 2000W
>> rectifiers running in parallel, nominally 8kW if running form a 240VAC
>> input source. Somewhat less on 208V.
>>
>> On Fri, Jul 15, 2016 at 7:06 AM, [email protected] <
>> [email protected]> wrote:
>>
>>> For the distribution bus, we use ICT. It's 1U and they have a version
>>> that support two inputs in 1U.
>>> It allows you to power cycle your loads. You can connect it to the
>>> rectifier of your choice.
>>> We get these from Winncom.
>>>
>>> If you don't need the full 2000W, Alpha makes a 2U 48Vdc Cordex HP 1.2kW
>>> 2RU
>>> ​. But you can't
>>> power cycle the loads.​ You can order these direct or from
>>> Winncom/Tessco.
>>>
>>> .
>>>
>>> On Thu, Jul 14, 2016 at 9:34 PM, Eric Kuhnke <[email protected]>
>>> wrote:
>>>
>>>> Looked, but the original FlatPack is not dense enough, the FlatPack2
>>>> and HE models are much smaller...  I am figuring out if a design for a POP
>>>> will fit in a single 45U rack with A and B power, each rectifier setup
>>>> needs to be 3U to 4U height maximum.
>>>>
>>>> On Thu, Jul 14, 2016 at 10:52 AM, Peter Kranz <[email protected]>
>>>> wrote:
>>>>
>>>>> I’d give ebay a scan, usually there are a few flatpack units there..
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> *Peter Kranz*www.UnwiredLtd.com <http://www.unwiredltd.com/>
>>>>> Desk: 510-868-1614 x100
>>>>> Mobile: 510-207-0000
>>>>> [email protected]
>>>>>
>>>>>
>>>>>
>>>>> *From:* Af [mailto:[email protected]] *On Behalf Of *Eric Kuhnke
>>>>> *Sent:* Monday, July 11, 2016 4:10 PM
>>>>> *To:* [email protected]
>>>>> *Subject:* [AFMUG] Anyone purchased an Eltek rectifier system
>>>>> recently?
>>>>>
>>>>>
>>>>>
>>>>> Looking for a ballpark price estimate off list on this:
>>>>>
>>>>>
>>>>> http://www.eltek.com/detail_products.epl?id=1142848&cat=24677&k1=&k2=&k3=&k4=&close=1
>>>>>
>>>>> It has a distribution bus/fuse/breaker panel in the top 1U, the bottom
>>>>> 1U populated with 4 x 2000W rectifiers.
>>>>>
>>>>> Or something else equivalent that is 2U to max 3U in size, 8kW rated
>>>>> at 230/240VAC input.
>>>>>
>>>>>
>>>>
>>>
>>
>

Reply via email to